Dear all
we are facing a problem with the mention thermostate tc303-3a2dpms. the thermostate does not restore pervious set temp value during power loss and restore
if some one have all hidden parameters details of this thermostae kindly share.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-12-29 05:41 AM
Hello,
This is the answer I got from the manufacturer a while ago:
The TC303-3A2DPMS (standalone) temperature setpoint will revert back to the default value after power is restored. This is per design.
"hidden parameters" 01 to 11 do not include default setpoint parameters/temperature adjustment.
Pat
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-12-29 05:41 AM
Hello,
This is the answer I got from the manufacturer a while ago:
The TC303-3A2DPMS (standalone) temperature setpoint will revert back to the default value after power is restored. This is per design.
"hidden parameters" 01 to 11 do not include default setpoint parameters/temperature adjustment.
Pat