Kamstrup 603 for glycol doesn't read energy, volume and flow

Field Devices Forum

Collaborate with a community of professionals and find answers and discuss anything related to the Field Devices (Sensors, Thermostats, Valves & Actuators and more)

ld94
Lieutenant JG
Lieutenant JG
0 Likes
4
719

Kamstrup 603 for glycol doesn't read energy, volume and flow

Hello everyone!

I'm having an issue with a Kamstrup for glycol: it doesn't read energy, volume and flow.
The % of the glycol given to Kamstrup before buying it was 55. On site the % has never been lower than 56/57 and in the first months it was around 60%: can the difference between the concentration set on the water meter and the actual one leading to this reading error?

Thank you in advance.

KR,
LD

Tags (1)
4 Replies 4
MikaelKrantz
Spock Spock
Spock
0 Likes
1
710

Re: Kamstrup 603 for glycol doesn't read energy, volume and flow

Lets see if I got this correct:

As long as it was about 60%, the energy calculation did work, but now, when it got down to like 56%, the reading do no longer work, and you get no flow indication?

Tags (1)
Troy_Wecker
Ensign Ensign
Ensign
0 Likes
1
693

Re: Kamstrup 603 for glycol doesn't read energy, volume and flow

The metering portion of the system uses sound waves bounced from the inside walls of the pipe.   If the sound cannot make it through the fluid then it cannot read flow.  Flow and temperatures are needed for energy reading.   There could be an issue with obstruction of the sound due to the concentration of glycol.   The speed at which the sound travels in a fluid also changes with the fluid composition.  It could affect accuracy but not significantly, repeatability usually is more significant and eliminates any accuracy issues.  Troubleshooting with help of the Schneider Customer Care Center is the first step and there is also the option of contacting Kamstrup at the e-mail on their website.

Tags (1)
ld94
Lieutenant JG
Lieutenant JG
0 Likes
0
588

Re: Kamstrup 603 for glycol doesn't read energy, volume and flow

Yes, you got it right.
I said to the installer to verify all the wirings and connections.

Tags (1)
ld94
Lieutenant JG
Lieutenant JG
0 Likes
0
587

Re: Kamstrup 603 for glycol doesn't read energy, volume and flow

@Troy_Wecker  Thank you Troy.
I'm trying to solve this with both SE support and Kamstrup since I cannot go on-site.