Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84863members
354353posts

How to measure the flow on PIBCV valve?

Field Devices Forum

Collaborate with a community of professionals and find answers and discuss anything related to the Field Devices (Sensors, Thermostats, Valves & Actuators and more)

Solved
Diego_Ramirez
Ensign
Ensign
5
3002

How to measure the flow on PIBCV valve?

Hello all,

 

Could someone indicate me please how do I measure the flow on the PIBCV valves using the PT ports?

Tags (1)

Accepted Solutions
Simon_Firth
Ensign Ensign
Ensign
0
2975

Re: How to measure the flow on PIBCV valve?

Hi, Measuring the flow is a relatively complex topic using the P-T ports and actually varies depending on which type (size/design) of valve we are using.

 

Document: F-28105 describes in detail the exact process for verifying the pressure and flow through all the DN10-250 valves.

F-27984 is the equivalent document for the 1/2" to 10" valves in the US with units of measurement in PSI and GPM

 

Basically, on the smaller valves, DN10 to DN32 (3/8" to 1-1/4") then the two P-T ports available are only used to verify the working pressure supplied to the valve is at the needed minimum level for the differential pressure regulator to work effectively.  If you do have the needed working pressure available, then you can be assured that the flow for any percentage setting scale on the valve is accurate and according to a document F-28130. This  F-28130 document declares the flow for any stroke limit (ie. flow setting considering the valve stroke limit is dependant on the set point setting).

 

For the larger valves with three test ports  where we are able to measure the full pressure drop across both the pressure regulator and the control valve portion of the valve as well as at the point in-between these components, then these pressures tapping's / readings are used alongside a table of effective Kvs to calculate the flow.. The comprehensive document guides: F-28105 Metric units / F-27984 - US units have these tables of effective Kvs/Cvs but there is also a simpler doc F-28088 available for just the DN40-250 valves.

 

 

Mr Valve

See Answer In Context

Attachments
Tags (1)
greg_peterson_s
Crewman Crewman
Crewman
0 Likes
0
1500

Re: How to measure the flow on PIBCV valve?

Please refer to SmartX PIBCV Pressure and Flow Verification F-27984 which you can be used with your commission/balancing agency. Here is the link.

 

https://ecoxpert.se.com/search?documentUUID=010b9c88-9c29-426b-a372-877c6fa54af2&title=PIBCV%20Smart...

 

Best Regards,

 

Greg Peterson

See Answer In Context

Tags (1)
5 Replies 5
Ted_Roman
Sisko Sisko
Sisko

Re: How to measure the flow on PIBCV valve?

@Diego_Ramirez 

 

Should be able to use ports if required to verify flow the same as balancing valve. 

 

https://www.contractingbusiness.com/service/article/20870767/service-clinic-how-to-measure-flow-thro... 

 

Flow setpoint is set with dial on actuator.

 

Best regards,

Ted

Tags (1)
Simon_Firth
Ensign Ensign
Ensign
0
2976

Re: How to measure the flow on PIBCV valve?

Hi, Measuring the flow is a relatively complex topic using the P-T ports and actually varies depending on which type (size/design) of valve we are using.

 

Document: F-28105 describes in detail the exact process for verifying the pressure and flow through all the DN10-250 valves.

F-27984 is the equivalent document for the 1/2" to 10" valves in the US with units of measurement in PSI and GPM

 

Basically, on the smaller valves, DN10 to DN32 (3/8" to 1-1/4") then the two P-T ports available are only used to verify the working pressure supplied to the valve is at the needed minimum level for the differential pressure regulator to work effectively.  If you do have the needed working pressure available, then you can be assured that the flow for any percentage setting scale on the valve is accurate and according to a document F-28130. This  F-28130 document declares the flow for any stroke limit (ie. flow setting considering the valve stroke limit is dependant on the set point setting).

 

For the larger valves with three test ports  where we are able to measure the full pressure drop across both the pressure regulator and the control valve portion of the valve as well as at the point in-between these components, then these pressures tapping's / readings are used alongside a table of effective Kvs to calculate the flow.. The comprehensive document guides: F-28105 Metric units / F-27984 - US units have these tables of effective Kvs/Cvs but there is also a simpler doc F-28088 available for just the DN40-250 valves.

 

 

Mr Valve
Attachments
Tags (1)
john8479
Cadet
0 Likes
0
2547

Re: How to measure the flow on PIBCV valve?

Mathematically it is easy to see how, as the authority of a control valve is defined as: N = DPv / (DPv + DPc). Where: DPv = Pressure drop across a fully open control valve DPc = Pressure drop across the remainder of the circuit.
 
Tags (1)
Alfred69
Crewman
Crewman
0 Likes
0
1511

Re: How to measure the flow on PIBCV valve?


@mcdvoice survey wrote: 

Hello all,

 

Could someone indicate me please how do I measure the flow on the PIBCV valves using the PT ports?


The smaller valves, DN10 to DN32 (3/8" to 1-1/4") then the two P-T ports available are only used to verify the working pressure supplied to the valve is at the needed minimum level for the differential pressure regulator to work effectively. If you do have the needed working pressure available, then you can be assured that the flow for any percentage setting scale on the valve is accurate and according to a document F-28130.

Tags (1)
greg_peterson_s
Crewman Crewman
Crewman
0 Likes
0
1501

Re: How to measure the flow on PIBCV valve?

Please refer to SmartX PIBCV Pressure and Flow Verification F-27984 which you can be used with your commission/balancing agency. Here is the link.

 

https://ecoxpert.se.com/search?documentUUID=010b9c88-9c29-426b-a372-877c6fa54af2&title=PIBCV%20Smart...

 

Best Regards,

 

Greg Peterson