How many SP90’s can I connect under one network ?

Field Devices Forum

Collaborate with a community of professionals and find answers and discuss anything related to the Field Devices (Sensors, Thermostats, Valves & Actuators and more)

Solved
Esperanto
Lieutenant JG
Lieutenant JG
0 Likes
2
856

How many SP90’s can I connect under one network ?

Hello,

 

Could you please give me guidance to size SP90 network?

 

Best regards

Espé

Tags (1)

Accepted Solutions
CraigEl
Administrator Administrator
Administrator

Re: How many SP90’s can I connect under one network ?

This probably depends on whether Modbus or BACnet is being used. Since it doesn't state the unit load of the device, it's best to assume a UL of 1 and therefore a maximum of 32 devices.

 

This is also noted on page 7 the Product Manual

 

See Answer In Context

2 Replies 2
CraigEl
Administrator Administrator
Administrator

Re: How many SP90’s can I connect under one network ?

This probably depends on whether Modbus or BACnet is being used. Since it doesn't state the unit load of the device, it's best to assume a UL of 1 and therefore a maximum of 32 devices.

 

This is also noted on page 7 the Product Manual

 

CraigEl
Administrator Administrator
Administrator

Re: How many SP90’s can I connect under one network ?

I've created a Knowledge Base article that provides further guidance on this.