Diverting application for 3 way valve

Field Devices Forum

Collaborate with a community of professionals and find answers and discuss anything related to the Field Devices (Sensors, Thermostats, Valves & Actuators and more)

Gingko_Elec
Lieutenant JG
Lieutenant JG
0 Likes
1
432

Diverting application for 3 way valve

Does Schneider have 3-way diverting valve DN50 for heat recovery?

 

V321 starts with DN65 but this is a little too big, the flow rate is calling for a Kvs better matching a DN50 size.

 

Thanks

Tags (1)
1 Reply 1
DavidChild
Sisko Sisko
Sisko
0 Likes
0
427

Re: Diverting application for 3 way valve

Hi,

 

What's the flow rate and pressure drop?

 

Or, do you know the calculated KVs already?

 

DN50's are generally going to be screwed at that size, but yes we do diverting/mixing valves at that size.

If the KVs is indicating closer to DN50, then the controllability will be better than a DN65.

 

The catalogue, also would be a good place to look in for the EMEA/APAC:

 

https://ecoxpert.se.com/search?documentUUID=5b0bb0c7-3f2b-445d-a313-d5240f84fa7e&title=2021%20Valves...