Standar pemasangan

Expert on Demand for Standards & Regulations

Solved
HelvinHermanT
Captain Captain
Captain
0 Likes
3
655

Standar pemasangan

Pertanyaan dari Pak @reinierliman 

 

Nanya dong Pak klo standar di IEC soal pemasangan RCCB atau ELCB didlm sarana hotel, rumah sakit, kitchen, swimming pool dan sejenisnya itu based on IEC 60364 bukan ya Pak?

Tags (1)

Accepted Solutions
HelvinHermanT
Captain Captain
Captain
0 Likes
2
652

StandaRe: Standar pemasangan

Benar Pak. 

 

Standar pemasangan / Instalasi diatur pada seri standar IEC 60364.

Pada seri IEC tersebut terdapat beberapa standar instalasi untuk lokasi /aplikasi tertentu.

 

Standar tersebut secara berkala diadopsi modifikasi kedalam seri standar lokal Indonesia SNI 0225 (Standar National Indonesia).

 

Berikut beberapa SNI 0225 atau disebut PUIL (Panduan Umum Instalasi Listrik), yang mengacu ke IEC 60364 :

 

No SNI Judul IND Status
 SNI 0225-1: 2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 1: Pendahuluan, prinsip fundamental dan definisi Masih Berlaku
 SNI 0225-5-56: 2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 - Bagian 5-56: Pemilihan dan pemasangan peralatan listrik – Layanan Keselamatan Masih Berlaku
 SNI 0225-7-706:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 7-706 – Persyaratan untuk instalasi atau lokasi khusus – Lokasi konduktif dengan gerakan terbatas Masih Berlaku
 SNI 0225-5-521:2020 Persyaratan UmuPersyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 5-521: Pemilihan dan pemasangan peralatan listrik – Transformator distribusi Masih Berlaku
 SNI 0225-7-711:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 7-711 – Persyaratan untuk instalasi atau lokasi khusus – Pameran, pertunjukan dan stan Masih Berlaku
 SNI 0225-3: 2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 - Bagian 3: Asesmen karakteristik umum Masih Berlaku
 SNI 0225-5-51:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 5-51: Pemilihan dan pemasangan peralatan listrik – Aturan bersama Masih Berlaku
 SNI 0225-5-52: 2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 5-52: Pemilihan dan pemasangan peralatan listrik – Sistem perkawatan Masih Berlaku
 SNI 0225-5-54:2020 Persyaratan Umum Instalasi Listrik (PUIL) - Bagian 5-54: Pemilihan dan pemasangan peralatan listrik – Susunan pembumian dan konduktor proteksi Masih Berlaku
 SNI 0225-5-511:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 5-511: Pemilihan dan pemasangan peralatan listrik – Perangkat sakelar dan kendali (PSDK) voltase rendah – PSDK daya Masih Berlaku
 SNI 0225-5-523:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 5-523: Pemilihan dan pemasangan peralatan listrik – Transformator distribusi – Transformator distribusi jenis kering Masih Berlaku
 SNI 0225-7-713:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 7-713 – Persyaratan untuk instalasi atau lokasi khusus – Furnitur Masih Berlaku
 SNI 0225-7-740:2020 Persyaratan Umum Instalasi Listrik 2020 (PUIL 2020) – Bagian 7-740: Persyaratan untuk instalasi dan lokasi khusus – Instalasi listrik temporer untuk bangunan, gawai hiburan dan gerai pada pasar raya, taman hiburan dan sirkus (IEC 60364-7-740:2000, MOD) Masih Berlaku
 SNI 0225-7-790:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 7-790: Persyaratan untuk instalasi atau lokasi khusus – Ketentuan untuk berbagai ruang dan instalasi khusus Masih Berlaku
 SNI 0225-7-704:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 –Bagian 7-704 – Persyaratan untuk instalasi atau lokasi khusus – Instalasi di lokasi konstruksi dan pembongkaran Masih Berlaku
 SNI 0225-7-703:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 7-703: Persyaratan untuk instalasi atau lokasi khusus – Ruangan dan kabin berisi pemanas sauna (IEC 60364-7-703:2004, MOD) Masih Berlaku
 SNI 0225-7-702:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 7-702: Persyaratan untuk instalasi atau lokasi khusus – Kolam renang dan air mancur Masih Berlaku
 SNI 0225-7-701:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 7-701: Persyaratan untuk instalasi atau lokasi khusus – Lokasi berisi bak atau dus (IEC 60364-7-701:2006, MOD) Masih Berlaku
 SNI 0225-5-514:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 5-514: Pemilihan dan pemasangan peralatan listrik – Perangkat sakelar dan kendali (PSDK) voltase rendah – Stasiun pengisian kendaraan listrik (SPKL) Masih Berlaku
 SNI 0225-5-513:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 5-513: Pemilihan dan pemasangan peralatan listrik – Perangkat sakelar dan kendali (PSDK) voltase rendah – Sistem berumbung busbar (SBB) Masih Berlaku
 SNI 0225-5-512:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 5-512: Pemilihan dan pemasangan peralatan listrik – Perangkat sakelar dan kendali (PSDK) voltase rendah – PSDK yang dimaksudkan untuk dioperasikan oleh orang awam (DBO) Masih Berlaku
 SNI 0225-5-55:2020 Persyaratan Umum Instalasi Listrik (PUIL) – Bagian 5-55: Pemilihan dan pemasangan peralatan listrik – Peralatan lain (IEC 60364-5-55:2016, MOD) Masih Berlaku
 SNI 0225-4-44:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 4-44: Proteksi untuk keselamatan – Proteksi terhadap gangguan voltase dan gangguan elektromagnetik (IEC 60364-4-44:2015, MOD) Masih Berlaku
 SNI 0225-4-43:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 4-43: Proteksi untuk keselamatan – Proteksi terhadap arus lebih (IEC 60364-4-43:2008, MOD) Masih Berlaku
 SNI 0225-4-41:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 4-41: Proteksi untuk keselamatan – Proteksi terhadap kejut listrik (IEC 60364-4-41:2017, MOD) Masih Berlaku
 SNI 0225-7-705:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 7-705: Persyaratan untuk instalasi atau lokasi khusus – Kompleks pertanian dan hortikultura Masih Berlaku
 SNI 0225-7-708:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 7-708: Persyaratan untuk instalasi atau lokasi khusus – Lapangan karavan, lapangan kemah dan lokasi sejenis Masih Berlaku
 SNI 0225-7-709:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 7-709 – Persyaratan untuk instalasi atau lokasi khusus – Marina dan lokasi sejenis Masih Berlaku
 SNI 0225-7-722: 2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 7-722 – Persyaratan untuk instalasi atau lokasi khusus – Suplai untuk kendaraan listrik Masih Berlaku
 SNI 0225-5-522:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 5-522: Pemilihan dan pemasangan peralatan listrik – Transformator distribusi – Transformator distribusi jenis terendam minyak mineral Masih Berlaku
 SNI 0225-7-710:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 7-710: Persyaratan untuk instalasi atau lokasi khusus – Lokasi medis Masih Berlaku
 SNI 0225-7-712:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 7-712: Persyaratan untuk instalasi atau lokasi khusus – Sistem suplai daya fotovoltaik surya (PV) Masih Berlaku
 SNI 0225-9:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 9: Pengusahaan instalasi listrik Masih Berlaku
 SNI 0225-8-2:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 8-2: Instalasi listrik voltase rendah prosumer Masih Berlaku
 SNI 0225-2:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 - Bagian 2: Desain instalasi listrik Masih Berlaku
 SNI 0225-5-53-2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 5-53: Pemilihan dan pemasangan peralatan listrik – Gawai proteksi untuk keselamatan, isolasi, penyakelaran, kendali dan pemantauan (IEC 60364-5-53:2019, MOD) Masih Berlaku
 SNI 0225-8-1:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 8-1: Aspek fungsional – Efisiensi Energi (IEC 60364-8-1:2019, MOD) Masih Berlaku
 SNI 0225-5-510:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 5-510: Pemilihan dan pemasangan peralatan listrik – Peralatan listrik Masih Berlaku

 

@HendySE @AP @Andry

 

 

See Answer In Context

Tags (1)
3 Replies 3
HelvinHermanT
Captain Captain
Captain
0 Likes
2
653

StandaRe: Standar pemasangan

Benar Pak. 

 

Standar pemasangan / Instalasi diatur pada seri standar IEC 60364.

Pada seri IEC tersebut terdapat beberapa standar instalasi untuk lokasi /aplikasi tertentu.

 

Standar tersebut secara berkala diadopsi modifikasi kedalam seri standar lokal Indonesia SNI 0225 (Standar National Indonesia).

 

Berikut beberapa SNI 0225 atau disebut PUIL (Panduan Umum Instalasi Listrik), yang mengacu ke IEC 60364 :

 

No SNI Judul IND Status
 SNI 0225-1: 2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 1: Pendahuluan, prinsip fundamental dan definisi Masih Berlaku
 SNI 0225-5-56: 2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 - Bagian 5-56: Pemilihan dan pemasangan peralatan listrik – Layanan Keselamatan Masih Berlaku
 SNI 0225-7-706:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 7-706 – Persyaratan untuk instalasi atau lokasi khusus – Lokasi konduktif dengan gerakan terbatas Masih Berlaku
 SNI 0225-5-521:2020 Persyaratan UmuPersyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 5-521: Pemilihan dan pemasangan peralatan listrik – Transformator distribusi Masih Berlaku
 SNI 0225-7-711:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 7-711 – Persyaratan untuk instalasi atau lokasi khusus – Pameran, pertunjukan dan stan Masih Berlaku
 SNI 0225-3: 2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 - Bagian 3: Asesmen karakteristik umum Masih Berlaku
 SNI 0225-5-51:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 5-51: Pemilihan dan pemasangan peralatan listrik – Aturan bersama Masih Berlaku
 SNI 0225-5-52: 2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 5-52: Pemilihan dan pemasangan peralatan listrik – Sistem perkawatan Masih Berlaku
 SNI 0225-5-54:2020 Persyaratan Umum Instalasi Listrik (PUIL) - Bagian 5-54: Pemilihan dan pemasangan peralatan listrik – Susunan pembumian dan konduktor proteksi Masih Berlaku
 SNI 0225-5-511:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 5-511: Pemilihan dan pemasangan peralatan listrik – Perangkat sakelar dan kendali (PSDK) voltase rendah – PSDK daya Masih Berlaku
 SNI 0225-5-523:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 5-523: Pemilihan dan pemasangan peralatan listrik – Transformator distribusi – Transformator distribusi jenis kering Masih Berlaku
 SNI 0225-7-713:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 7-713 – Persyaratan untuk instalasi atau lokasi khusus – Furnitur Masih Berlaku
 SNI 0225-7-740:2020 Persyaratan Umum Instalasi Listrik 2020 (PUIL 2020) – Bagian 7-740: Persyaratan untuk instalasi dan lokasi khusus – Instalasi listrik temporer untuk bangunan, gawai hiburan dan gerai pada pasar raya, taman hiburan dan sirkus (IEC 60364-7-740:2000, MOD) Masih Berlaku
 SNI 0225-7-790:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 7-790: Persyaratan untuk instalasi atau lokasi khusus – Ketentuan untuk berbagai ruang dan instalasi khusus Masih Berlaku
 SNI 0225-7-704:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 –Bagian 7-704 – Persyaratan untuk instalasi atau lokasi khusus – Instalasi di lokasi konstruksi dan pembongkaran Masih Berlaku
 SNI 0225-7-703:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 7-703: Persyaratan untuk instalasi atau lokasi khusus – Ruangan dan kabin berisi pemanas sauna (IEC 60364-7-703:2004, MOD) Masih Berlaku
 SNI 0225-7-702:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 7-702: Persyaratan untuk instalasi atau lokasi khusus – Kolam renang dan air mancur Masih Berlaku
 SNI 0225-7-701:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 7-701: Persyaratan untuk instalasi atau lokasi khusus – Lokasi berisi bak atau dus (IEC 60364-7-701:2006, MOD) Masih Berlaku
 SNI 0225-5-514:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 5-514: Pemilihan dan pemasangan peralatan listrik – Perangkat sakelar dan kendali (PSDK) voltase rendah – Stasiun pengisian kendaraan listrik (SPKL) Masih Berlaku
 SNI 0225-5-513:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 5-513: Pemilihan dan pemasangan peralatan listrik – Perangkat sakelar dan kendali (PSDK) voltase rendah – Sistem berumbung busbar (SBB) Masih Berlaku
 SNI 0225-5-512:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 5-512: Pemilihan dan pemasangan peralatan listrik – Perangkat sakelar dan kendali (PSDK) voltase rendah – PSDK yang dimaksudkan untuk dioperasikan oleh orang awam (DBO) Masih Berlaku
 SNI 0225-5-55:2020 Persyaratan Umum Instalasi Listrik (PUIL) – Bagian 5-55: Pemilihan dan pemasangan peralatan listrik – Peralatan lain (IEC 60364-5-55:2016, MOD) Masih Berlaku
 SNI 0225-4-44:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 4-44: Proteksi untuk keselamatan – Proteksi terhadap gangguan voltase dan gangguan elektromagnetik (IEC 60364-4-44:2015, MOD) Masih Berlaku
 SNI 0225-4-43:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 4-43: Proteksi untuk keselamatan – Proteksi terhadap arus lebih (IEC 60364-4-43:2008, MOD) Masih Berlaku
 SNI 0225-4-41:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 4-41: Proteksi untuk keselamatan – Proteksi terhadap kejut listrik (IEC 60364-4-41:2017, MOD) Masih Berlaku
 SNI 0225-7-705:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 7-705: Persyaratan untuk instalasi atau lokasi khusus – Kompleks pertanian dan hortikultura Masih Berlaku
 SNI 0225-7-708:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 7-708: Persyaratan untuk instalasi atau lokasi khusus – Lapangan karavan, lapangan kemah dan lokasi sejenis Masih Berlaku
 SNI 0225-7-709:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 7-709 – Persyaratan untuk instalasi atau lokasi khusus – Marina dan lokasi sejenis Masih Berlaku
 SNI 0225-7-722: 2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 7-722 – Persyaratan untuk instalasi atau lokasi khusus – Suplai untuk kendaraan listrik Masih Berlaku
 SNI 0225-5-522:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 5-522: Pemilihan dan pemasangan peralatan listrik – Transformator distribusi – Transformator distribusi jenis terendam minyak mineral Masih Berlaku
 SNI 0225-7-710:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 7-710: Persyaratan untuk instalasi atau lokasi khusus – Lokasi medis Masih Berlaku
 SNI 0225-7-712:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 7-712: Persyaratan untuk instalasi atau lokasi khusus – Sistem suplai daya fotovoltaik surya (PV) Masih Berlaku
 SNI 0225-9:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 9: Pengusahaan instalasi listrik Masih Berlaku
 SNI 0225-8-2:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 8-2: Instalasi listrik voltase rendah prosumer Masih Berlaku
 SNI 0225-2:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 - Bagian 2: Desain instalasi listrik Masih Berlaku
 SNI 0225-5-53-2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 5-53: Pemilihan dan pemasangan peralatan listrik – Gawai proteksi untuk keselamatan, isolasi, penyakelaran, kendali dan pemantauan (IEC 60364-5-53:2019, MOD) Masih Berlaku
 SNI 0225-8-1:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 8-1: Aspek fungsional – Efisiensi Energi (IEC 60364-8-1:2019, MOD) Masih Berlaku
 SNI 0225-5-510:2020 Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 5-510: Pemilihan dan pemasangan peralatan listrik – Peralatan listrik Masih Berlaku

 

@HendySE @AP @Andry

 

 

Tags (1)
HelvinHermanT
Captain Captain
Captain
0 Likes
1
647

Re: StandaRe: Standar pemasangan

Untuk tahun 2021 ini sedang dilakukan  penyusunan RSNI dibawah ini : 

 

1. IEC 60364-7-701 “Low-voltage electrical installations – Part 7-701: Requirements for special installations or locations – Locations containing a bath or shower”
2. IEC 60364-7-714 “Low-voltage electrical installations –Part 7-714: Requirements for special installations or locations – External lighting installations”
3. IEC 60364-7-715 “Low-voltage electrical installations –Part 7- 715: Requirements for special installations or locations – Extralow voltage lighting installations”
Tags (1)
HelvinHermanT
Captain Captain
Captain
0 Likes
0
456

Re: StandaRe: Standar pemasangan

Pada tanggal 22 Oktober 2021, Kementerian Energi dan Sumberd Daya Mineral Republik Indonesia  sudah melaksanakan Rapat Konsensus yang dihadiri oleh Anggota Komite Teknis KT 91-03 (KTPUIL) dan berbagai stakeholder yang terkait lainnya termasuk Badan Standardisasi Indonesia & Dirjen Ketenagalistrikan. Rapat konsensus diselenggarakan oleh Direktorat Jenderal Ketenagalistrikan - Kementrian EDSM.

 

Rapat Konsensus untuk 2 standard PUIL  :

 

1. RSNI Bagian 7-715 : Persyaratan untuk Instalasi atau lokasi khusus - Instalasi pencahayaan voltase extra rendah (IEC 60364-7-715:2022)

 

2. RSNI Bagian 8-3 : Aspek Fungsional - Operasi Instalasi Listrik Prosumer (IEC TS 60364-8-3:2020).

 

 

 

Schneider Electric Indonesia diwakili oleh Helvin Herman Tirtadjaja turut berpartisipasi dalam Proses penyusunan hingga Rapat Konsensus.

 

 

Sertifikat Rapat Konsensus KTPUIL.jpeg