Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84519members
353745posts

In Ecodial, Why the "conductor sizes of cable" are always limited below 300 mm2

EcoStruxure Power Design Forum

Collaborate with your peers on Electrical Network Design and Calculation Software(Ecodial, Electrical Calculation Tools) - ask questions and get answers from Schneider Electric experts and peers. Share your experience.

Solved
Christopher_D
Crewman
Crewman
0 Likes
1
1337

In Ecodial, Why the "conductor sizes of cable" are always limited below 300 mm2

Hello, 

In an electrical network calculation, Ecodial is proposing the ‘conductor sizes of the cable’ not more than 300 mm2 and is there any specific reasons to do that? Can you please provide some comments on this.

Tags (1)

Accepted Solutions
Genghiz
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
0
1332

Re: Cable and Conductor Sizing

Hello,

Thanks for your interest on this subject “conductor sizing of the cables.”

 

In Ecodial, the “conductor sizing algorithm for cable” is done in accordance with the IEC 60364-5-52 standard.

 

While the application is entirely following the “the current carrying capacity tables” from the IEC 60364-5-52 for various installation methods, and these tables are mostly limited to have the current carrying capacities defined only up to 300 mm2.

 

Current Carrying Capacities for Various Conductor SizesCurrent Carrying Capacities for Various Conductor Sizes

 

 

So, the application is also having this limitation in sizing of conductors only up to 300 mm2 cross sectional area; On the other hands the application is already capable to size the conductors up to 630 mm2 cross sectional area - as per the respective tables for the installation references F and G.

 

 

See Answer In Context

Tags (1)
1 Reply 1
Genghiz
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
0
1333

Re: Cable and Conductor Sizing

Hello,

Thanks for your interest on this subject “conductor sizing of the cables.”

 

In Ecodial, the “conductor sizing algorithm for cable” is done in accordance with the IEC 60364-5-52 standard.

 

While the application is entirely following the “the current carrying capacity tables” from the IEC 60364-5-52 for various installation methods, and these tables are mostly limited to have the current carrying capacities defined only up to 300 mm2.

 

Current Carrying Capacities for Various Conductor SizesCurrent Carrying Capacities for Various Conductor Sizes

 

 

So, the application is also having this limitation in sizing of conductors only up to 300 mm2 cross sectional area; On the other hands the application is already capable to size the conductors up to 630 mm2 cross sectional area - as per the respective tables for the installation references F and G.

 

 

Tags (1)