How to get the right cable sizing of a circuit from the Ecodial

EcoStruxure Power Design Forum

Collaborate with your peers on Electrical Network Design and Calculation Software(Ecodial, Electrical Calculation Tools) - ask questions and get answers from Schneider Electric experts and peers. Share your experience.

Solved
Anvar_B
Cadet
0 Likes
2
1171

How to get the right cable sizing of a circuit from the Ecodial

Can you please help me to understand how do I optimize cable sizing?

Tags (1)

Accepted Solutions
Genghiz
Lt. Commander Lt. Commander
Lt. Commander

Re: How to get the "optimum cable sizing of a circuit" from the Ecodial

Thanks for your interest in Ecodial. 

 

The optimum sizing of conductors (cable) for a circuit can be explained by constructing a Simple Network with the "HVLV transformer as a source" and connected to a LV Switchboard. The same Switchboard is also connected a 'Passive load circuit."

 

 

Sample Network.PNG

 [the above image shows the Simple Network, as explained above]

 

 

INPUTS:

 

At the 'Passive load' circuit, the LOAD and CABLE component characteristics should be provided as the "INPUT properties" to the application. These inputs are considered for sizing the 'conductors (cable) of the circuit.' 

 

LOAD CABLE 
load inputs.png

 

cable inputs.png

 

 

 

OUTPUTS: 

 

Once after calculating the network, the output of the calculations (solution) can be seen at the 'Details' section of the application, and also on the single line diagram of the network. 

 

"Solutions" view will help us to see the sizing results on the SLD single line diagram.  After selecting the circuit component on the SLD, the "Properties" sections will also helps us to see the solutions. After selecting the circuit component on the SLD, the "Details" sections will also helps us to see the solutions.
Output_Properties_SLD.png Output_Properties.png Output_Properties_Details.png

 

 

 

See Answer In Context

Tags (1)
2 Replies 2
Genghiz
Lt. Commander Lt. Commander
Lt. Commander

Re: How to get the "optimum cable sizing of a circuit" from the Ecodial

Thanks for your interest in Ecodial. 

 

The optimum sizing of conductors (cable) for a circuit can be explained by constructing a Simple Network with the "HVLV transformer as a source" and connected to a LV Switchboard. The same Switchboard is also connected a 'Passive load circuit."

 

 

Sample Network.PNG

 [the above image shows the Simple Network, as explained above]

 

 

INPUTS:

 

At the 'Passive load' circuit, the LOAD and CABLE component characteristics should be provided as the "INPUT properties" to the application. These inputs are considered for sizing the 'conductors (cable) of the circuit.' 

 

LOAD CABLE 
load inputs.png

 

cable inputs.png

 

 

 

OUTPUTS: 

 

Once after calculating the network, the output of the calculations (solution) can be seen at the 'Details' section of the application, and also on the single line diagram of the network. 

 

"Solutions" view will help us to see the sizing results on the SLD single line diagram.  After selecting the circuit component on the SLD, the "Properties" sections will also helps us to see the solutions. After selecting the circuit component on the SLD, the "Details" sections will also helps us to see the solutions.
Output_Properties_SLD.png Output_Properties.png Output_Properties_Details.png

 

 

 

Tags (1)
Genghiz
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
0
1149

Re: How to get the "optimum cable sizing of a circuit" from the Ecodial

Hello,

Here is also an example to see the calculation of conductor sizing for the given inputs. 

This article explains the conductor sizing based on the 'Theoretical algorithm' suggested by the IEC 60364-5-52 standard. I hope, this should add further value/answer to your query.