Help
  • Explore Community Expore Community
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Explore Community Explore Community
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • EcoStruxure Asset Advisor
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
    • EcoStruxure IT Help Center
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Diversity factors are not considered bug need to be fixed

EcoStruxure Power Design Forum

Schneider Electric support forum to share knowledge about installation and usage for Electrical Network Design and Calculation Software (Ecodial, Ecostruxure Power Design).

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution Software
  • EcoStruxure Power Design Forum
  • Diversity factors are not considered bug need to be fixed
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Commander Genghiz Commander
31
Karthikeyan1
Ensign Karthikeyan1 Ensign
4
Sayani_Sikdar
Sayani_Sikdar Schneider Alumni (Retired)
3
ArjunSwamy
ArjunSwamy Schneider Alumni (Retired)
1
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Power Design – Ecodial

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Power Design Forum
Solved
Ahmed2004
Crewman Ahmed2004
Crewman

Posted: ‎2023-04-08 02:35 PM . Last Modified: ‎2023-04-08 02:38 PM

0 Likes
12
1430
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-08 02:35 PM . Last Modified: ‎2023-04-08 02:38 PM

Diversity factors are not considered bug need to be fixed

The software doesnot reflect the upstream load current (Ib) based on the diversity factors that assigned for each busbars or each final load.

According to the above the software gives oversizing for the relavent cable and source based on those Ib(s) which is not correct (its not practicable to assigne the Ib for each upstream CB for the data entry field in the CB properties).

Please find below link to download the file for you review.

Used version 4.9.9 and 5

 

https://www.mediafire.com/file/6i0bctp3f2u0jbs/Test_to_SCh.eac/file

Labels
  • Labels:
  • Ecodial
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Genghiz
Commander Genghiz Commander
Commander

Posted: ‎2023-04-27 03:55 AM

0 Likes
2
1138
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-27 03:55 AM

Hello Ahmed,

In continuation with the acceptance of the issue “in retaining the right current values at the feeders” (while opening the project).  

 

As a workaround, It is suggested lock the values of Ib(A) at the circuit breakers during the normal design (before saving the project).

 

Use the lock to reatin the feeder current valueUse the lock to reatin the feeder current value

 

This may help you in avoiding the issue, while opening the project.

 

Regards,

Team - Ecodial Expert Support.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 12
Ahmed2004
Crewman Ahmed2004
Crewman

Posted: ‎2023-04-10 03:10 PM . Last Modified: ‎2023-04-10 03:27 PM

0 Likes
0
1324
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-10 03:10 PM . Last Modified: ‎2023-04-10 03:27 PM

many thanks for your reply, for more explination, the software do the following for the above example (Test to SCh.eac):

 

First issue:
a. The assigned KU for the final panel (L.DS01 and L.DS02) is 0.1 and for the panel (L.DS03) is 0.07 and the assigned KS for the submain panel (S01-DPR.) is 0.5, this means the total demand load for this panel should be 232 kVA as indicated in the software which is correct, but the upstream (Ib) for this panel it indicated on the software based on the KS and KU = 1 (Ib = 852A) based on the total connected load which is (590 kVA), which means the software neglect all the assigned factors, actually in this case the Ib at the CB (D.DPR) should be equal (335A), and the cable shall be sized accordingly, please be noted that, all the upstream panel have the same issues upto the transformer which gives huge oversizing.


Second issue:

a. If I create a new SLD, the software can consider all the KS and KU in the frist time of calculation of the upstream Ib, but If I closed the calculation file and open it again the software shows the KS and KU but doesnot consider them in the upstrem Ib claculation. (please refer to (New Test to SCh 01.eac) at the below link).

https://www.mediafire.com/file/e6doxoiu8y8ywmx/New_Test_to_SCh_01.eac/file

 

b. When I tried to solve the above issue temperory, just I switched the main CB (transfomer downstream CB) OFF then ON, accordingly the software updating the upstram Ib, this is also very big issue need to be solved from roots.


Third issue:

a. For the file that I sent in the main post (Test to SCh.eac), the above solution (which mentioned on the second issue (b) is not working), since the software doesnot updating the Ib after switching the main CB OFF then ON, which means the software have differnt behaviors with each calculation file.

 

Forth issue:

I have another file that the SLD built based on 50hz, and its not possible to change the frequiency to 60Hz, where this also possible for the other files (I will attach this file latter on, since its not ready with me now).

 

Sorry for this long text, but every body knows that, the ecodial software is very trusted by many of design orgnization and consultanty, but the above issues make it (in some how in the current version) unreliable.

Reply

Link copied. Please paste this link to share this article on your social media post.

Genghiz
Commander Genghiz Commander
Commander

Posted: ‎2023-04-12 02:29 AM

0 Likes
2
1305
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-12 02:29 AM

Hello Ahmed,

Thanks for reaching us through the EcoStruxure Power Design – Forum.

 

The Ks & Ku:

These factors are mainly used in the software to size the ‘source’ of the network.

The simultaneity (Ks-diversity) and the Ku (utilization) can be momentary for an electrical network.

This should not impact the ‘size of the cable (or) the protection selection.’

 

Suggestion:

The usage of these factor along with operating mode; will help you to understand the worst-case scenario. Whereas all the loads can be working together (Ks=1) and all the loads may be consuming on its defined values (Ku=1). So, the usage of these factors should not impact the “cable and protection sizing.”

 

Application behaviour:

As reviewed by our colleagues from different countries (during the product development), this has been accepted as expected behaviour.

 

Thanks & Regards,

Team - Ecodial Expert Support

Reply

Link copied. Please paste this link to share this article on your social media post.

Ahmed2004
Crewman Ahmed2004
Crewman

Posted: ‎2023-04-12 08:16 AM . Last Modified: ‎2023-04-12 08:50 AM

In response to Genghiz
0 Likes
1
1298
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-12 08:16 AM . Last Modified: ‎2023-04-12 08:50 AM

Hi Genghiz,

 

its my honerd to be one of the members of the EcoStruxure power design forum


I agree with you for the above sentance regarding to the KU and KS "This should not impact the ‘size of the cable (or) the protection selection" , this is totally right for the final load only, but for the upstrem feeder cables and CB's upto the source, this cannot considred right, since those factos are finally considred as reduction factors.

 

I'm awaiting your feedback for the two examples that are attached above.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Ahmed2004
Crewman Ahmed2004
Crewman

Posted: ‎2023-04-13 01:34 PM

0 Likes
0
1282
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-13 01:34 PM

Please find attched files for more calrification about this issues (Second issue)

https://www.mediafire.com/file/iu6scoavk0nn4al/New_Test_to_SCh_01.eac.zip/file

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Ahmed2004
Crewman Ahmed2004
Crewman

Posted: ‎2023-04-13 02:02 PM . Last Modified: ‎2023-04-13 02:02 PM

0 Likes
0
1279
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-13 02:02 PM . Last Modified: ‎2023-04-13 02:02 PM

Here is the same example after playing with the Ks and Ku but its ok even after closing and opening the project !!!!

(which means the software have differnt behaviors with each calculation file) !!

 

https://www.mediafire.com/file/9vj3vbux7rz9t8f/New_Test_to_SCh_02.zip/file

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Genghiz
Commander Genghiz Commander
Commander

Posted: ‎2023-04-24 01:37 AM

In response to Ahmed2004
0 Likes
0
1167
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-24 01:37 AM

Hello Ahmed,

 

Thanks for your understanding on the usage of the ‘Ks & Ku factors.’

As you agreed the there is no impact of these factors on the ‘final load circuits’ and they will be sized for the full rating of the loads.

 

For the question on the feeders & the source circuits.

These factors cannot be considered as reduction factors…due to the operating scenario of the worst case (Full consumption of loads {ku=1}and when they will be working together {ks=1} as group of loads.) needs to be considered to size them.

 

Regards,

Team – Ecodial Expert Support.

Reply

Link copied. Please paste this link to share this article on your social media post.

Ahmed2004
Crewman Ahmed2004
Crewman

Posted: ‎2023-04-26 06:12 AM . Last Modified: ‎2023-04-26 06:13 AM

0 Likes
0
1150
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-26 06:12 AM . Last Modified: ‎2023-04-26 06:13 AM

Hi Genghiz,

 

Can you please check all the attcehed files and aso the pdf's, also please check the Ib for each case, accordingly we can discuss (there is something wrong, and we need your advises !!)

Reply

Link copied. Please paste this link to share this article on your social media post.

Genghiz
Commander Genghiz Commander
Commander

Posted: ‎2023-04-27 02:04 AM

0 Likes
0
1143
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-27 02:04 AM

Hello Ahmed,

Thanks for your efforts in explaining the scenario.

 

Agreed:

  • This is an issue during the file opening.
  • Yes, you have revealed this issue, that is occurring at the time of file opening.
  • The application has good/expected behaviour during the normal operation of the network.
  • Whereas the reopening of the project has not maintained, some input for the power calculation.

 

Next Steps:

  • This scenario is explained to the software development team and reported for the fix/improvement.
  • We will keep you posted on the status.

 

Thanks & Regards,

Team – Ecodial Expert Support.

Reply

Link copied. Please paste this link to share this article on your social media post.

Genghiz
Commander Genghiz Commander
Commander

Posted: ‎2023-04-27 03:55 AM

0 Likes
2
1139
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-27 03:55 AM

Hello Ahmed,

In continuation with the acceptance of the issue “in retaining the right current values at the feeders” (while opening the project).  

 

As a workaround, It is suggested lock the values of Ib(A) at the circuit breakers during the normal design (before saving the project).

 

Use the lock to reatin the feeder current valueUse the lock to reatin the feeder current value

 

This may help you in avoiding the issue, while opening the project.

 

Regards,

Team - Ecodial Expert Support.

Reply

Link copied. Please paste this link to share this article on your social media post.

Ahmed2004
Crewman Ahmed2004
Crewman

Posted: ‎2023-04-27 06:22 AM

0 Likes
0
1133
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-27 06:22 AM

Hi Genghiz,

Thanks for your support, waiting for the fix of the software.

Reply

Link copied. Please paste this link to share this article on your social media post.

SI_part_EcoXpert_BMSMaster
Lieutenant | EcoXpert Master SI_part_EcoXpert_BMSMaster Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2023-07-15 01:23 AM

In response to Genghiz
0 Likes
0
432
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-07-15 01:23 AM

Thanks for clarifying these doubts. Have faced them, and thanks to tour replies in this thread. was able to satisfactorily deal with it. However, please advise your L1/L2 ecostruure power design support team to be atleast responsive. Too many queries to them dont even get a response. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Genghiz
Commander Genghiz Commander
Commander

Posted: 1 week ago

In response to Genghiz
0 Likes
0
54
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: 1 week ago

Hello,

 

During the file opening and maintaining the 'given value' for the Ku & Ks has been fixed, and delivered as part of the 'International version.'

 

This can be verified at the version - EcoStruxure Power Design - Ecodial INT V5.02

 

Thanks & Regards,

Team - Ecodial Expert Support

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc