U-Heigh not in DCO api

EcoStruxure IT forum

A support forum for Data Center Operation, Data Center Expert, and EcoStruxure IT product users to share knowledge on installation, configuration, and general product use.

Solved
shloa
Ensign
Ensign
0 Likes
6
685

U-Heigh not in DCO api

Hi,

 

I asked the person in charge of the DCO software to add U-Height.

He did that, but I can not see that value when I access the API.

 

Can U-Height be available through the API? how?

 

Thanks.

Tags (1)

Accepted Solutions
Jef
Captain Captain
Captain
0 Likes
0
660

Re: U-Heigh not in DCO api

'/assets/search' would not return the info you need, you would need to use GET /assets/{asset-id}

please see my illustration above.

 

Kind regards,

Jef

See Answer In Context

Tags (1)
6 Replies 6
gsterling
Commander Commander
Commander
0 Likes
4
679

Re: U-Heigh not in DCO api

Hello, which version of DCO are you using?

 

I believe the below highlighted item is the U-height of the server I queried via the DCO rest api (DCO 8.3.2 or newer).

 
Tags (1)
shloa
Ensign
Ensign
0 Likes
0
673

Re: U-Heigh not in DCO api

9.2.4

Tags (1)
gsterling
Commander Commander
Commander
0 Likes
2
667

Re: U-Heigh not in DCO api

Sorry, looks like the picture I shared did not paste properly. I re-added the screenshot.

 

This value is present in both DCO and ITA and appears to represent U-Height of the device.

 

U-Height.JPG

Tags (1)
Jef
Captain Captain
Captain
0 Likes
0
664

Re: U-Heigh not in DCO api

Hi Shlomit, 

 

Yes, it is possible to get the assets/device 'Unit height' value via the REST api. ( https://<ITA server IP>api/current/docs/index.html )

 

Here is an illustration:
a device with Unit height 2
Capture_jf1.JPG

go to https://<ITA server IP>api/current/docs/index.html

GET /assets/{asset-id}

enter your asset-id 

and then hit the 'Try it out!'
in the Response Body window, device 'unitHeight' should be displayed:
Capture_jf2.JPG

 

Kind regards,

Jef

 

Tags (1)
shloa
Ensign
Ensign
0 Likes
1
663

Re: U-Heigh not in DCO api

I go to https://.../api/v8.1/assets/search, no height,  I get only the attributes:

 


{
"id": "",
"type": "",
"location": " ",
"parentId": "",
"parentName": "",
"parentType": "",
"roomId": "",
"roomName": "",
"roomType": "",
"cageName": "",
"rackName": "",
"barcode": "",
"description": "",
"name": "",
"manufacturer": "",
"modelName": "",
"partNumber": "",
"serialNumber": "",
"customPropertyKeys": "",
"customPropertyValues": "",
"luceneSearchScore": 
}

 

Thanks a lot.

Tags (1)
Jef
Captain Captain
Captain
0 Likes
0
661

Re: U-Heigh not in DCO api

'/assets/search' would not return the info you need, you would need to use GET /assets/{asset-id}

please see my illustration above.

 

Kind regards,

Jef

Tags (1)