Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
    • EcoStruxure IT Help Center
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Important Announcement: Community Back to Full Functionality

Dear Members, we are thrilled to announce that our Community is back to full functionality and that posts publication is now enabled again! We appreciate your patience during the last weeks. Learn more about our Community Guidelines. Thank you, Schneider Electric Community Team.

Powertag Power readings are not correctly shown in DCE

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Powertag Power readings are not correctly shown in DCE
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Jef
Captain Jef Captain
79
APC_Steve
Commander APC_Steve Commander
55
gsterling
Commander gsterling Commander
50
Cory_McDonald
Lt. Commander Cory_McDonald Lt. Commander
15
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 08:58 PM

0 Likes
3
661
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 08:58 PM

Powertag Power readings are not correctly shown in DCE

This question was originally posted on DCIM Support by ozgur on 2019-07-25


 

Hello community,

 

We are having trouble with reading power values via powertags in DCE . We added 4 acti 9 smartlink devices in DCE with 20 powertags connected wirelessly to each of them. 

When access directly to web server of acti 9 smartlinks we can read the power values as shown at the screenshot below ; 

 

 

But in DCE ; link status is online , data looks corrupted .

 

Devices are being added in modbus tcp device add section.For device type i can only choose " Acti9 Smartlink Modbus " to make it online.

I have downloaded and imported the two DDF files from DDF library portal which are related with Acti9 devices. Slave address of smartlinks looks impossible to change they are all 255 . İ couldnt at least. When i delete the other discovered smartlinks and tried out just one with same 255 slave address also couldnt have success in power readings. I think slave address section is not the subject in this situation.

We use powertag 1560 and 1570 models. Smartlink devices are upgraded to latest 2.2.7 firmware. Data Center Expert is not yet upgraded to R 7.6  .Its a phsiycal appliance running with delivery Release 7.4.1. 

I hope i could explain the problem. Any advice that you give me would be highly appreciated. 

Thanks in advance.

 

Best regards.

Ozgur.

(CID:147198240)

Labels
  • Labels:
  • Data Center Expert
  • DDF
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 08:58 PM

0 Likes
1
663
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 08:58 PM

This answer was originally posted on DCIM Support by Jake Hiltz on 2019-07-25


Hi Ozgur,

Because you are using Powertag sensors, I think you have an Acti9 Smartlink SI B or D.  In this case, you will want to use the "schneider_acti9_smartlinksid.xml" DDF which you can download from the DDF download page (it looks like you are using the DDF with the file named "schneider_acti9_smartlink.xml" - the names are so similar, this can be confusing).

In addition to using that DDF, you will want to enter the slave address of the Powertag sensor, not the Acti9 itself.  The Acti9 will assign the sensors the Modbus slave address automatically, so you will probably have to look in the Acti9 configuration to know which addresses go with which sensors.

From page 79 of the Smartlink SI D manual:  "Acti9 Smartlink SI D allocates dynamically, a slave number 150 through 169 for each of the 20 wireless communication devices (up to 20 wireless communication devices) that could be connected to the Acti9 Smartlink SI D."

 

Let us know if this resolves your issue.

Jake

(CID:147198453)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 08:58 PM

0 Likes
1
664
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 08:58 PM

This answer was originally posted on DCIM Support by Jake Hiltz on 2019-07-25


Hi Ozgur,

Because you are using Powertag sensors, I think you have an Acti9 Smartlink SI B or D.  In this case, you will want to use the "schneider_acti9_smartlinksid.xml" DDF which you can download from the DDF download page (it looks like you are using the DDF with the file named "schneider_acti9_smartlink.xml" - the names are so similar, this can be confusing).

In addition to using that DDF, you will want to enter the slave address of the Powertag sensor, not the Acti9 itself.  The Acti9 will assign the sensors the Modbus slave address automatically, so you will probably have to look in the Acti9 configuration to know which addresses go with which sensors.

From page 79 of the Smartlink SI D manual:  "Acti9 Smartlink SI D allocates dynamically, a slave number 150 through 169 for each of the 20 wireless communication devices (up to 20 wireless communication devices) that could be connected to the Acti9 Smartlink SI D."

 

Let us know if this resolves your issue.

Jake

(CID:147198453)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 08:58 PM

In response to DCIM_Support
0 Likes
0
663
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 08:58 PM

This comment was originally posted on DCIM Support by ozgur on 2019-07-25


Hi Jake,

Thank you very much for your help. Your information about adding powertags seperately with the same ip address of smartlink SI D,  but with unique slave address solved my issue. I tought that just adding smartlink will be enough for viewing powertags running behind it and i now see it was so wrong. Finally i will submit the project. It was urgent.

Thanks a lot again.

😀

Best regards.

Ozgur.

(CID:147198584)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 08:59 PM

0 Likes
0
663
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 08:59 PM

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc