Hello All, I have recently encountered a puzzling issue with a Netbotz 450. Connecting to it serially via terminal. The appliance hangs while booting up, see below:
The appliance hangs at Net: FCC1 ETHERNET
Note: appliance is operating with the latest firmware, date of manufacture: 2018/03/09.
Nothing loads after that. What might be causing this issue?
U-Boot 1.1.4 (Oct 31 2017 - 14:32:43)
MPC8248 Reset Status: External Soft, External Hard
MPC8248 Clock Configuration
- Bus-to-Core Mult 3x, VCO Div 4, 60x Bus Freq 16-50 , Core Freq 50-150
- dfbrg 0, corecnf 0x10, busdf 3, cpmdf 1, plldf 0, pllmf 3
- vco_out 400000000, scc_clk 100000000, brg_clk 100000000
- cpu_clk 300000000, cpm_clk 200000000, bus_clk 100000000
- pci_clk 33333333
CPU: MPC8248 (HiP7 Rev 14, Mask 1.0 1K50M) at 300 MHz
Watchdog enabled
I2C: ready
DRAM: 128 MB
FLASH: 64 MB
PCI Scan: Found Bus 0, Device 22, Function 0
PCI Scan: Found Bus 0, Device 22, Function 1
PCI Scan: Found Bus 0, Device 22, Function 2
In: serial
Out: serial
Err: serial
Net: FCC1 ETHERNET
(CID:134038009)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 12:17 AM . Last Modified: β2024-04-04 12:57 AM
Hi Thabos,
I've seen a few instances where the reset button has been stuck "in" and it can cause the boot to hang or the system to constantly reboot. My first suggestion is to get a paper clip and push in on the reset button and move it around a little to see if that resolves the issue.
Other than that, it might be a firmware issue. I'm not sure where these lines are in the boot process but if it gets past the u-boot load (where it says press any key within 10, 9, 8....) then I would suggest reflashing the firmware using the tftp flash procedure here:
Thanks,
Steve.
(CID:134038137)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 12:17 AM . Last Modified: β2024-04-04 12:57 AM
Hi Thabos,
I've seen a few instances where the reset button has been stuck "in" and it can cause the boot to hang or the system to constantly reboot. My first suggestion is to get a paper clip and push in on the reset button and move it around a little to see if that resolves the issue.
Other than that, it might be a firmware issue. I'm not sure where these lines are in the boot process but if it gets past the u-boot load (where it says press any key within 10, 9, 8....) then I would suggest reflashing the firmware using the tftp flash procedure here:
Thanks,
Steve.
(CID:134038137)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 12:17 AM . Last Modified: β2024-04-04 12:57 AM
Hi Steve
Thanks for the response, I'll check if the reset button is stuck. i have a feeling that might be the cause. π
as for where it says press any key within 10, 9, 8....). the boot procedure doesn't reach that point.
(CID:134038431)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 12:17 AM . Last Modified: β2023-10-22 03:19 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.