Netbotz 250 - Modbus Register Map

EcoStruxure IT forum

A support forum for Data Center Operation, Data Center Expert, and EcoStruxure IT product users to share knowledge on installation, configuration, and general product use.

Solved
dsantillan
Lieutenant
Lieutenant
0 Likes
2
507

Netbotz 250 - Modbus Register Map

Hello, 

 

I have been trying to poll modbus data from Netbotz 250 and slave Sensor Pods 150. Main module registers work ok. Explansion modules registers do not. Using reference JLER-AFTRPH_R1 Document 990-5851A

 

Units are using latest firmware.

 

Please let me know if there is a newer map to try, 

 

Thank you,

 

Douglas

Tags (1)

Accepted Solutions
TechieBala
Ensign Ensign
Ensign

Re: Netbotz 250 - Modbus Register Map

Hi @dsantillan Can you please try polling the Sensor Pod 150 current registers with offset of 6 and see if it helps? It appears that the modbus register map needs to be updated with the correct registers. 

You may also report this issue by contacting your country technical support team. 

See Answer In Context

Tags (1)
2 Replies 2
TechieBala
Ensign Ensign
Ensign

Re: Netbotz 250 - Modbus Register Map

Hi @dsantillan Can you please try polling the Sensor Pod 150 current registers with offset of 6 and see if it helps? It appears that the modbus register map needs to be updated with the correct registers. 

You may also report this issue by contacting your country technical support team. 

Tags (1)
dsantillan
Lieutenant
Lieutenant

Hello, Re: Netbotz 250 - Modbus Register Map

Hello,

 

Thank you for the reply. 

 

I decided to scan registers, indeed there is an offset of 6. Polling works having this in mind. 

 

Best regards,

 

Douglas

Tags (1)