Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

Close
Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82566members
350187posts

NetBotz 570 , connecting digital inputs

EcoStruxure IT forum

A support forum for Data Center Operation, Data Center Expert, and EcoStruxure IT product users to share knowledge on installation, configuration, and general product use.

Solved
DCIM_Support
Picard
Picard
0 Likes
8
579

NetBotz 570 , connecting digital inputs

This question was originally posted on DCIM Support by Alex Rente on 2018-12-12


Hello experts,

I already ask a question concerning this topic, but got recently confused by a collegue. My question is, do I connect a 0/24V DigitalOutput directly on Nr 9 OR on Nr 10 with an upstream voltageconverter(0-24V to 0-5V):

In the describtion from the NetBotz is written:

9.) 4-20 mA Inputs: Provides 24 VDC for connecting third-party sensors with an input current range from 4 to 20 mA.

10.) Sensor ports: Used for connecting APC by Schneider Electric sensors, third-party dry-contact sensors, and standard third-party 0-5 V sensors. (See “Additional Options” on page 3 for details on sensor options.) Third-party dry-contact state sensors require the NetBotz Dry Contact Cable (NBES0304). Standard third-party 0-5 V sensors require the NetBotz 0-5 V Sensor Cable (NBES0305). NBRK0450/550 - 5/24 VDC (50mA). NBRK0570 - 5/24 VDC (200mA).

 

 

with best regards

Alex

(CID:137110964)


Accepted Solutions
DCIM_Support
Picard
Picard
0 Likes
4
579

Re: NetBotz 570 , connecting digital inputs

This answer was originally posted on DCIM Support by spezialist on 2018-12-12


Dear Alex Rente,

Ok, this simplest task, unfortunately, is not solved only by =SE= products.

Solution 1 (best): buy NetBotz Dry Contact Cable - 15 ft. (NBES0304) for $39.99 and connect it to the universal sensor inputs (from Nr 10). Find an discrete/relay output in your 3rd party equipment, that will close/open its contacts (i.e., the output instead of your 24/0V DC voltage output). Connect it together and then your NetBotz appliance will determine the discrete state of your 3rd party equipment.

Solution 2: buy NetBotz Dry Contact Cable - 15 ft. (NBES0304) for $39.99 and connect it to the universal sensor inputs (from Nr 10). Buy a low-voltage intermediate relay with one pair of switching contacts. Connect the coil of this relay to the voltage output 24/0V DC of your 3rd party equipment. Connect the switching contacts of this relay to the cable NBES0304 and then your NetBotz appliance will determine the discrete state of your 3rd party equipment.

Both of the above solutions are the best in terms of electromagnetic protection, since your NetBotz appliance will be electrically isolated from your 3rd party equipment. It is very important in industrial conditions.

Therefore, I do not suggest you buy a NetBotz 0-5V Cable - 15 ft. (NBES0305) cable for analog solutions for $69.99. And then use a resistive voltage divider to connect it to your 3rd paty equipment, as described in your past question. Such a solution is dangerous, as the NetBotz appliance can fail due to electromagnetic surges and an overvoltage at the universal sensor input.

With respect.

(CID:137111037)

See Answer In Context

8 Replies 8
DCIM_Support
Picard
Picard
0 Likes
1
580

Re: NetBotz 570 , connecting digital inputs

This answer was originally posted on DCIM Support by spezialist on 2018-12-12


Dear Alex Rente,

There are many options and wiring diagrams. However, practically, 24V DC output (from Nr 7) can be used in conjunction with relay outputs Relay1 and Relay2.

On the other hand, the Current inputs (from Nr 9) and universal sensor inputs (from Nr 10) do not provide for the connection of power supply. On the contrary, universal sensor ports provide power for sensors, for example, for an temperature/humidity AP9335TH digital sensor.

In order to help you, we need to understand your task well.

If you have more questions, please ask.

With respect.

(CID:137111004)

DCIM_Support
Picard
Picard
0 Likes
0
580

Re: NetBotz 570 , connecting digital inputs

This comment was originally posted on DCIM Support by Alex Rente on 2018-12-12


Hello=)

Ok, you may misunderstood me. I got a sensor (Device 1 is working, true=24V, wrong=0V) which i want to connect to my NetBotz.

I do not need power-supply for that sensor , i just want to process the input-signal on/off.

with best regards

Alex

(CID:137111014)

DCIM_Support
Picard
Picard
0 Likes
4
580

Re: NetBotz 570 , connecting digital inputs

This answer was originally posted on DCIM Support by spezialist on 2018-12-12


Dear Alex Rente,

Ok, this simplest task, unfortunately, is not solved only by =SE= products.

Solution 1 (best): buy NetBotz Dry Contact Cable - 15 ft. (NBES0304) for $39.99 and connect it to the universal sensor inputs (from Nr 10). Find an discrete/relay output in your 3rd party equipment, that will close/open its contacts (i.e., the output instead of your 24/0V DC voltage output). Connect it together and then your NetBotz appliance will determine the discrete state of your 3rd party equipment.

Solution 2: buy NetBotz Dry Contact Cable - 15 ft. (NBES0304) for $39.99 and connect it to the universal sensor inputs (from Nr 10). Buy a low-voltage intermediate relay with one pair of switching contacts. Connect the coil of this relay to the voltage output 24/0V DC of your 3rd party equipment. Connect the switching contacts of this relay to the cable NBES0304 and then your NetBotz appliance will determine the discrete state of your 3rd party equipment.

Both of the above solutions are the best in terms of electromagnetic protection, since your NetBotz appliance will be electrically isolated from your 3rd party equipment. It is very important in industrial conditions.

Therefore, I do not suggest you buy a NetBotz 0-5V Cable - 15 ft. (NBES0305) cable for analog solutions for $69.99. And then use a resistive voltage divider to connect it to your 3rd paty equipment, as described in your past question. Such a solution is dangerous, as the NetBotz appliance can fail due to electromagnetic surges and an overvoltage at the universal sensor input.

With respect.

(CID:137111037)

DCIM_Support
Picard
Picard
0 Likes
0
579

Re: NetBotz 570 , connecting digital inputs

This comment was originally posted on DCIM Support by Alex Rente on 2018-12-12


Hello,

i made a little scetch..

Does that match your thoughts ?

I agree with you, that point 3 is not good. Point 2 is the same like point 1 but the relais is outside?!

And it would be very nice if you could explain me why i cant just directly connect it to Nr9. Just from logic thinking I would say it is not good, because it measures current and not voltage, fruthermore we have no defined state at 0V.

If my scetch is right, i just have another little question

 

with best regards

Alex

 

(CID:137111075)

DCIM_Support
Picard
Picard
0 Likes
0
579

Re: NetBotz 570 , connecting digital inputs

This comment was originally posted on DCIM Support by spezialist on 2018-12-12


Dear Alex Rente,

From your comments:

Does that match your thoughts ?

Absolutely correct.

I agree with you, that point 3 is not good. Point 2 is the same like point 1 but the relais is outside?!

But an intermediate relay can be placed inside your 3rd party equipment. That is, Solution 1 uses the built-in relay of your 3rd party equipment, and Solution 2 uses an additional relay. Electrically both solutions are exactly the same.

And it would be very nice if you could explain me why i cant just directly connect it to Nr9. Just from logic thinking I would say it is not good, because it measures current and not voltage, fruthermore we have no defined state at 0V.

That's right, Current inputs (from Nr 9) measure the DC current flowing through them. Accordingly, the connection scheme of current sensors is completely different. For example, like this:

With respect.

(CID:137111172)

DCIM_Support
Picard
Picard
0 Likes
0
579

Re: NetBotz 570 , connecting digital inputs

This comment was originally posted on DCIM Support by Alex Rente on 2018-12-12


Thank you very much. That was very helpful !!

My last question considering solution 1 and 2. I mean, I could just accept the fact that it works, but I want to know why ^^ ? When I bridge the contacts, what voltage or which level I will get then on the input and why?

 

Best regards

Alex

EDIT: Ahhh ich got it. I understood it 😃 Again: Thanks a lot

 

(CID:137111248)

DCIM_Support
Picard
Picard
0 Likes
0
579

Re: NetBotz 570 , connecting digital inputs

This comment was originally posted on DCIM Support by spezialist on 2018-12-12


Dear Alex Rente,

I mean, I could just accept the fact that it works, but I want to know why ^^ ? When I bridge the contacts, what voltage or which level I will get then on the input and why?

Ok, it's very simple, I think my little picture will answer your question:

More details about the connection and characteristics of the NBES0304 can be found in my answer .

With respect.

(CID:137111374)

DCIM_Support
Picard
Picard
0 Likes
0
580

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.