Posted: 2021-05-21 08:57 AM
Now we have progressed from DCO to ITA I am exploring new features like the asset visuals. I have started a row of racks but have hit a problem where some racked kit has the asset visuals tile for adding/editing the images and some kit has no tile so I cannot add any visuals?
See screenshots.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-05-21 10:11 AM
Hello Nigel
One item of note regarding asset visuals is that it pertains to server assets. Other asset types are not supported, at least not yet. This is mentioned on the asset visual page (https://helpcenter.ecostruxureit.com/hc/en-us/articles/360006854398-Asset-Visuals)
.. Is the device which is not displaying the asset visuals tile a non-server device?
Regards
Greg Sterling
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-05-21 10:11 AM
Hello Nigel
One item of note regarding asset visuals is that it pertains to server assets. Other asset types are not supported, at least not yet. This is mentioned on the asset visual page (https://helpcenter.ecostruxureit.com/hc/en-us/articles/360006854398-Asset-Visuals)
.. Is the device which is not displaying the asset visuals tile a non-server device?
Regards
Greg Sterling
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.