Easy UPS MIB for SMV2000CAI

EcoStruxure IT forum

A support forum for Data Center Operation, Data Center Expert, and EcoStruxure IT product users to share knowledge on installation, configuration, and general product use.

brianmus21
Cadet
0 Likes
1
281

Easy UPS MIB for SMV2000CAI

I just bought a new SMV2000CAI with a SNMP module. However I cannot find the MIB from Webpage of SE.

 

Anyone can provide me the MIB? I tried with 3 PS MIB. however some of the translation is incorrect.

 

 

snap-ups.jpg

Tags (1)
1 Reply 1
JohnBT
Ensign Ensign
Ensign
0 Likes
0
278

Re: Easy UPS MIB for SMV2000CAI

Hello,

 

The APV9602 card conforms with RFC1628.  You can download the RFC1628 mib online or you can try the attached MIB.  

 

John