Easy UPS 3S RS-485 port issues
  • EcoStruxure IT forum
  • Re: Easy UPS 3S RS-485 port issues
  • Subscribe to RSS Feed
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
108
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
Back to EcoStruxure IT forum
jaimegut
Crewman jaimegut Crewman
Posted: ‎2022-07-31 07:40 PM . Last Modified: ‎2022-10-19 12:44 AM
4708
Hello community !
Need some support in getting an Easy UPS 3S talking via the Modbus RS-485 port.  Here is the FW version
Rectifier: V55.008.002
Inverter: V55.008.002
I've tried both with a Panel Server PAS600 and PAS800 with similar results when trying to use ModScan to read register values.
ModBus Set values:
Address: 001
Com Mode: ASCII (have tried RTU as well with exact same results)
Baud Rate: 9600
Com set: Normal
There's a tutorial video on YouTube that shows exactly how some colleagues in Schneider Electric Spain did this and I've replicated the steps with no luck.
https://www.youtube.com/watch?v=XdSHnuA9-i0
In the video, the narrator even shows the exact function code they are reading and the registers, no success when I try the same.
At some point I even tried flipping the + and - wires on the back of the UPS to try and rule out that as a possible issue.
Looking for some additional ideas, maybe a FW issue or something else.
Any ideas are welcome.
I've read similar previous posts below:
https://community.se.com/t5/EcoStruxure-Building-Operation/Modbus-integration-of-a-3S-UPS-on-EBO/m-p...
Replies 19
jaimegut
Posted: ‎2022-08-01 03:33 AM
In response to Smith904
I should have mentioned that I already had the ModBus register map and tried different register reads.
Any other suggestions?
tjlaw
Lt. Commander tjlaw Lt. Commander
Posted: ‎2022-08-10 10:06 PM
4546
HI,
Just wondering if you tried connect directly via USB to RS485 to the UPS and scanned using ModScan? Or maybe you can share the error you have while using ModScan through Panel Server?
BR,
TJ
jaimegut
Posted: ‎2022-08-30 12:50 PM
In response to tjlaw
4389
I completely missed that there was activity on this thread, my bad.
Actually I have tried USB directly to the RS-485 port as well and scanned using ModScan, nothing seems to be talking out of the RS-485 terminals.
Using the PanelServer is the same (either via the embedded webpage of the panel server or using ModScan going through the panel server), there's nothing but "no comms" status being returned.
I've been careful to follow all the settings listed in the ModBus manual (stop bits, parity, default baud rate, etc.).  I even went as far as flipping the + / -  on the back of the Easy UPS to try and see if that would present any different results (both when using the panel server or communicating directly).  Nothing shows any signs of that port actually doing anything unfortunately.
The registers that I'm trying to read from are a few easy points to verify that communication is even possible.
For example,
Input Voltage on each phase, address 10012, 10013, 10014 using read function 0x03
Input Frequency on each phase, address 10018, 10019, 10020 using read function 0x03
I'm pretty sure that the unit I have is not communicating via the RS-485 port.
Dominique38
Ensign Dominique38 Ensign
Posted: ‎2022-09-08 05:57 AM . Last Modified: ‎2022-09-08 05:58 AM
In response to jaimegut
4284
Be sure that menu "Communication Set " is set to Normal.
Take care about modbus address sent to the UPS, depends of tool used
With Modscan, you must add one to register address
Exemple, for address 2710 hexa format requested, you have to set either 10001 decimal format or 2711 haxa format
After that, Easy 3S is working fine with modbus requests
jaimegut
Posted: ‎2022-09-08 06:06 AM
In response to Dominique38
4278
Thank you for the response @Dominique38 ,,, I did verify this already see attached document.
And yes, I have considered the offset based on the Modbus protocol to make sure that I wasn't polling an incorrect register.
Dominique38
Posted: ‎2022-09-08 06:14 AM
4274
See my Modscan request:
is there an answer form the Easy ??
jaimegut
Posted: ‎2022-09-08 06:53 AM
4271
@Dominique38
Let me ask something, so I can replicate exactly what you are doing.
1. Are you using panel server in between the Easy UPS and Modscan ?  ( That's the setup I have and have also tried going direct via a USB to RS-485 converter)   I am asking so I can replicate the method you are doing.
2. In the Easy UPS, under "ModBus Set", what setting are you using (RTU / ASCII) ?
Dominique38
Posted: ‎2022-09-08 07:24 AM
4264
I use a small USB/RS485 converter 2 wires form Aliexpress, like this one:
https://fr.aliexpress.com/item/1005003032516569.html
Then i use RTU mode and 9600bd (works bettter than 19200), 8 bits/no parity/no flow control/one stop
Shaun
Commander Shaun Commander
Posted: ‎2022-09-08 07:26 AM
4263
Hi @Dominique38
That looks reasonable to me -the next bytes look like a modbus exception so it looks like communication is good (eg, both ends are speaking to each other, they just don't like the answer)
Could you try requesting less than 125 registers?  The modbus map is non-contiguous (there's "reserved blocks" eg at 10056-70).  How that's handled varies between devices - some only complain if you start the request in empty space, some won't allow you to address empty space at all.
I haven't been able to test this myself yet, but this is the only difference I can see between your examples and the spanish video, so it may be worth trying.
  Shaun
Dominique38
Posted: ‎2022-09-08 07:33 AM
In response to Shaun
4260
Hi Shaun,
i did not see the video
Here is the answer of the 125 register: the Easy is able to reply the 125 registers contiguous even if some of them are reserved
tjlaw
Posted: ‎2022-09-08 07:49 AM
Do you mind sharing the UPS firmware version you communicating with? Compared with the firmware version encountered by @jaimegut
BR,
TJ
jaimegut
Posted: ‎2022-09-08 07:59 AM
Just replicated everything you've suggested,
MODBUS Message TIME-OUT is the response being sent back to ModScan (Pictures shows both 125 registers and 10 registers attempted to be read)
I'm striking out with this particular unit left and right
Shaun
Posted: ‎2022-09-08 08:09 AM . Last Modified: ‎2022-09-08 08:09 AM
4243
@Dominique38 , sorry, I got you and the customer confused.
That does seem to rule out that idea though, thanks for that.
Dominique38
Posted: ‎2022-09-08 08:43 AM
4234
I can not check UPS firmware now, i'll do it next Monday.
Check your USB/RS485 converter...??
jaimegut
Posted: ‎2022-09-08 09:02 AM
4231
I'm using:
https://www.gearmo.com/shop/usb-to-rs485-rs422-converter-with-ftdi-chip/
Hasn't been a problem on other devices 😀
Dominique38
Posted: ‎2022-09-11 11:54 PM
4170
Here is UPS firmware version:
jaimegut
Posted: ‎2022-09-12 06:11 AM
I'm sourcing another USB to RS485 converter, will have it in a day or two.
I'll provide an update to see if that changes anything, however I doubt this is the problem since the results have been the same using an EcoStruxure Panel (PAS600) server to try reach its registers through TCP-IP and the panel server as well was not able to establish communications with the UPS unit.
jaimegut
Posted: ‎2022-09-20 06:17 AM
@Dominique38
Sorry, it took me a week to source the component to be similar to the one you are using.
Just tried it out, no difference in the results.
Changed Baud Rate, flipped the +/- wires, changed from RTU to ASCII (both on the UPS and on ModScan), did several things to make sure it wasn't a bad item on the physical wiring or a setting oversight.
I'm back to thinking that this particular unit I have is not able to communicate over the RS-485 port in the back.
afecomt
Crewman afecomt
Posted: ‎2024-09-27 03:04 AM
updating firmware sometimes solve the problem
tenemos muchos problemas con este ups.
schenider support requested us logs with Tuner software. lets see
This is a heading
