Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82573members
350203posts

Cooling unit simulate impact

EcoStruxure IT forum

A support forum for Data Center Operation, Data Center Expert, and EcoStruxure IT product users to share knowledge on installation, configuration, and general product use.

Solved
Venkat
Ensign Ensign
Ensign
0 Likes
5
1755

Cooling unit simulate impact

Hi,

 

One of our cusotmer having DCO -  v8.3.2 and we have simulated the Cooling Impact and 5 Cooling Units and found the same racks showing impact for all the Cooling units.  

 

If we change the power capacity to predicted power value in preference, there is no impact showing for the Cooling Units.

 

The screen shot attached for your kind reference.

 

Thanks - K.Venkat

 

 

 

 

 

Attachments
Tags (1)

Accepted Solutions
ATrabert
Lieutenant JG Lieutenant JG
Lieutenant JG
0 Likes
0
1693

Re: Cooling unit simulate impact

Hi Venkat,

Glad you're seeing more expected values, I should have been more specific but I was asking for estimated load of room (eg Floor PDU load) and the Cooling Capactiy of the cooling units. CFM would also be relevant.

 

The higher the floor pdu load (which includes the rack pdu load), the greater the simulated impact of 1 or more cooling units failing/being turned off.

 

cooling properties.jpg

 

 
 

 

See Answer In Context

Tags (1)
Jef
Captain Captain
Captain
0 Likes
0
1662

Re: Cooling unit simulate impact

Hi Venkat,

It seems to be bug (somewhere in the setup), changing power strategy to Predicted Power should not break Impact calculations. I cannot find any reason why this may happen in your setup, so I have added this to our backlogs for debugging.

For the time being you might want to switch to Adjusted Nameplate strategy when running the simulate impact.

Kind regards,

Jef

See Answer In Context

Tags (1)
5 Replies 5
Venkat
Ensign Ensign
Ensign
0 Likes
3
1736

Re: Cooling unit simulate impact

Dears

 

Any Suggestion please.

 

Thanks - K.Venkat

Tags (1)
ATrabert
Lieutenant JG Lieutenant JG
Lieutenant JG
2
1734

Re: Cooling unit simulate impact

Hi Venkat,

What is the cooling capacity of the 3 cooling units individually/combined and how much estimated load and/or predicted load is being used right now?

 

I noticed only one cooling unit was off, since there are still 2 more in the room, they can most likely handle the additional cooling load for the 3rd unit. This is why you are not really seeing any cooling impact.  Also if the power usage is low, this would also explain why you are not seeing much if any cooling impact.

 

What happens when you turn off 2 or all 3 units? 

Tags (1)
Venkat
Ensign Ensign
Ensign
0 Likes
1
1695

Re: Cooling unit simulate impact

Hi ATrabert,

 

Thanks. 

 

Now I am getting the simulation impact values for more racks, while de-activate the 1 or 2 Cooling Units. (Predicted power / Adjusted name plate) 

 

There is no measured power value for Cooling Unit and only the Estimated load each Unit having 81kW  as name plate and cooling power. The adjusted name plate consider as 45kW for each Unit.

 

Thanks - K.Venkat.

Tags (1)
ATrabert
Lieutenant JG Lieutenant JG
Lieutenant JG
0 Likes
0
1694

Re: Cooling unit simulate impact

Hi Venkat,

Glad you're seeing more expected values, I should have been more specific but I was asking for estimated load of room (eg Floor PDU load) and the Cooling Capactiy of the cooling units. CFM would also be relevant.

 

The higher the floor pdu load (which includes the rack pdu load), the greater the simulated impact of 1 or more cooling units failing/being turned off.

 

cooling properties.jpg

 

 
 

 

Tags (1)
Jef
Captain Captain
Captain
0 Likes
0
1663

Re: Cooling unit simulate impact

Hi Venkat,

It seems to be bug (somewhere in the setup), changing power strategy to Predicted Power should not break Impact calculations. I cannot find any reason why this may happen in your setup, so I have added this to our backlogs for debugging.

For the time being you might want to switch to Adjusted Nameplate strategy when running the simulate impact.

Kind regards,

Jef

Tags (1)