Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

Close
Important Announcement: WELCOME to the Schneider Electric Community! We have moved to a new address: community.se.com — bookmark it today and contact SchneiderCommunity.Support@se.com if you have any questions!
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82750members
350528posts

Cooling Configuration - Alarm

EcoStruxure IT forum

A support forum for Data Center Operation, Data Center Expert, and EcoStruxure IT product users to share knowledge on installation, configuration, and general product use.

Solved
Venkat
Ensign Ensign
Ensign
0 Likes
2
963

Cooling Configuration - Alarm

Hi team,

 

One of our customer, we need to show the below DCIM Feature points for Cooling configuration.

 

We didn't find out the Alarms / recommended actions as follow up the below scenario. 

 

Ability to alarm cooling configuration issues and provide recommended actions. For example, a room has no perforated tiles for the Computer Room Air Conditioning (CRAC) unit airflow (one or more CRACs have been added to the floor but no perforated tiles have been added), or there is no perforated tile airflow (one or more perforated tiles have been added to the room but no CRACs have been provided to supply any airflow).

 

Kindly suggest us with screenshots to explain customer end.

 

Thanks & Regards,

 

K.Venkat.

Tags (1)

Accepted Solutions
Jef
Captain Captain
Captain
0 Likes
1
942

Re: Cooling Configuration - Alarm

Hi Venkat,

The notification concerning adding perforated tiles may be displayed if there should be modeled downflow CRACS in the room.

Modeling downflow CRACS requires raised floor and adding some perforated tiles.  To configure raised floor, right click on your room/data center > Properties > Floor , and then enable the 'Raised floor' option and define 'Floor height'.

 

In the following illustration I have only modeled a Downflow CRAC:

Capture_1.JPG

then I will go ahead and set the room/Floor properties:

Capture_2.JPG

and add Perforated Floor Tile(s):
Capture_3.JPG

 

Kind regards,

Jef

See Answer In Context

Tags (1)
2 Replies 2
Jef
Captain Captain
Captain
0 Likes
1
943

Re: Cooling Configuration - Alarm

Hi Venkat,

The notification concerning adding perforated tiles may be displayed if there should be modeled downflow CRACS in the room.

Modeling downflow CRACS requires raised floor and adding some perforated tiles.  To configure raised floor, right click on your room/data center > Properties > Floor , and then enable the 'Raised floor' option and define 'Floor height'.

 

In the following illustration I have only modeled a Downflow CRAC:

Capture_1.JPG

then I will go ahead and set the room/Floor properties:

Capture_2.JPG

and add Perforated Floor Tile(s):
Capture_3.JPG

 

Kind regards,

Jef

Tags (1)
Venkat
Ensign Ensign
Ensign
0 Likes
0
933

Re: Cooling Configuration - Alarm

Thanks Jef.

 

Simulated with customer exiting solution and got the same result.

 

Regards - K.Venkat

Tags (1)