Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

set alarm on battery temperature

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • set alarm on battery temperature
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:46 PM . Last Modified: ‎2024-04-03 12:42 AM

0 Likes
3
2531
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:46 PM . Last Modified: ‎2024-04-03 12:42 AM

set alarm on battery temperature

How do I set an alarm on the battery temperature in an APC  Smart-UPS?

.1.3.6.1.4.1.318.1.1.1.2.2.2 is the battery temperature in celcius

Pretty sure the OID is listed above. I can view it in DCE, view the value, generate a static trend report, and so on, but those done by selecting the sensor from, "custom"... which isn't available when creating an alarm,  I need to configure alarms with this sensor. 

how do I do this ? 

(CID:148342614)

Labels
  • Labels:
  • Data Center Expert
  • DDF
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:46 PM . Last Modified: ‎2024-04-03 12:42 AM

0 Likes
0
2530
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:46 PM . Last Modified: ‎2024-04-03 12:42 AM

Dear Eric,

As far as I know, the UPS itself has got its self protection charging method which is called as Temperature Compensated Charging method if your UPS has got an internal batteries. The Charging of the batteries will be controlled by the UPS as per the temperature compensated charging method. 

The optimum operating temperature for a lead-acid battery is 20-25° C (68-77° F). Elevated temperature reduces longevity. As a guideline, every 8° C (15° F) rise in temperature will cut the battery life in half. A battery which would last for 4 years at 25° C (77° F), will only be good for 2 years if operated at 33° C (95° F). Keep in mind that the battery temperature inside your UPS will always be warmer than the ambient temperature of the location where the UPS is installed.

So in my opinion, setting the threshold for the UPS ambient temperature is recommended as the ambient temperature can be controlled by the Customer. If your UPS has an NMC with temperature probe connected to it to monitor the ambient temperature, then I suggest to create a Custom threshold for the ambient temperature probe reading. 

That being said, DCE already has a feature to create a customized threshold in DCE for any sensors values that you can see under view device sensors. I can see an option to create the Customized threshold for one of the Smart UPSs that I have. I can see Temperature option to click on and create the threshold. If possible, can you please share us the screen shot to know which options that you see when you are trying to create the threshold for battery temperature? Is the temperature threshold type grayed out?

 

I also noticed that the DCE has already got a device alarm notification for Smart UPS which has an internal batteries. See below. So in this case, the DCE will show an alarm when the Smart UPS battery temperature is abnormal. The threshold of the battery temperature depends upon the UPS model and its design. 

I hope this helps. 

Regards,

Bala

(CID:148342658)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:46 PM . Last Modified: ‎2024-04-03 12:42 AM

0 Likes
0
2530
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:46 PM . Last Modified: ‎2024-04-03 12:42 AM

Dear Eric Clark,

Please tell us, were you able to solve your question or not?

With respect.

(CID:148771893)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:46 PM . Last Modified: ‎2023-10-22 09:36 PM

0 Likes
0
2530
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:46 PM . Last Modified: ‎2023-10-22 09:36 PM

superhero.pngsuperhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore