"public_network_connection" table not synchronizing

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • "public_network_connection" table not synchronizing
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 01:40 AM . Last Modified: ‎2024-04-05 04:03 AM

0 Likes
12
1642
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 01:40 AM . Last Modified: ‎2024-04-05 04:03 AM

"public_network_connection" table not synchronizing

Hi,

I’m having synchronizing issues with the “public_network_connection” table.. I conducted several successful tests of changing the “state_flag” column to “changed”  for several devices in the “public_configuration_item” and “public_port_configuration” tables. No issues associating devices or creating/changing/removing port configurations on each device., but the cable connections are not syncing in the network connection table. I have been tasked with automating cable connections in a very large data center with more than 20,000 cables at each site. In approximately two years, this is the second time in two months this has happened.

I’ve made thousands of additions, changes, and removals with this table in the past with no issues, and I haven’t changed how I do anything.

I’m curious if this issue has been seen before? The other two tables are working fine, so it doesn’t appear to be an overall database issue. Perhaps something is locking the “public_network_connection” table? Here is a brief background of our environment: We have roughly 15,000 devices in the “public_configuration_item” table, over 30,000 records in the “public_port_configuration” table, and roughly 30,000 records in the network connection table. We are using an internal PostgreSQL database instance running on the same server as Data Center Operation. The server itself has maximum required specs.

 

Any reason as to why the network connection table would suddenly stop syncing properly? Any help would be greatly appreciated.

(CID:126172817)

Labels
  • Labels:
  • Data Center Operation
  • Tags:
  • bug
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 12
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 01:40 AM . Last Modified: ‎2024-04-05 04:03 AM

0 Likes
0
1641
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 01:40 AM . Last Modified: ‎2024-04-05 04:03 AM

Hi Thomas

What version of DCO are you using?

(CID:126173270)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 01:40 AM . Last Modified: ‎2024-04-05 04:03 AM

0 Likes
7
1641
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 01:40 AM . Last Modified: ‎2024-04-05 04:03 AM

Hi Thomas,

It is most likely (a tip from etl developer) they/devices are not associated yet, both source (device with start point) and target (device with end point) must have been associated first, otherwise they will not be sync'ed.

Kind regards

(CID:126173372)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 01:40 AM . Last Modified: ‎2024-04-05 04:03 AM

In response to DCIM_Support
0 Likes
0
1641
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 01:40 AM . Last Modified: ‎2024-04-05 04:03 AM

Well, I ran several tests of changing a device's status to "changed" to see if would switch back to "synced", and that was a success.. I also changed several port names, as well as adding an removing a port in the "public_port_configuration" table, and that was a success as well. So those tables appear to still work..

(CID:126173509)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 01:41 AM . Last Modified: ‎2024-04-05 04:03 AM

In response to DCIM_Support
0 Likes
0
1640
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 01:41 AM . Last Modified: ‎2024-04-05 04:03 AM

An update to above is that I thought the devices lost their association, so I changed the "state_flag" column to "changed" in the port configuration table to see if they would switch back to "synced", and 98% changed back to "synced"

(CID:126173526)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 01:41 AM . Last Modified: ‎2024-04-05 04:03 AM

In response to DCIM_Support
0 Likes
0
1640
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 01:41 AM . Last Modified: ‎2024-04-05 04:03 AM

Hi Thomas,
Would it be possible to share screen captures illustrating the issue & also showing the affected/relevant network connection/port configuration and 'not synced' problem. (if possible, please mask sensitive info such as IP add.), thanks.

Kind regards

 

(CID:126173802)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 01:41 AM . Last Modified: ‎2024-04-05 04:03 AM

In response to DCIM_Support
0 Likes
0
1640
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 01:41 AM . Last Modified: ‎2024-04-05 04:03 AM

Hi, thanks again for your response. Here are three screen captures showing a sample of connections in the "new" state.

 

(CID:126174475)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 01:41 AM . Last Modified: ‎2024-04-05 04:03 AM

In response to DCIM_Support
0 Likes
0
1640
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 01:41 AM . Last Modified: ‎2024-04-05 04:03 AM

Hi Thomas,

Many thanks for the images, but unfortunately they do not show what might be the issue. So I was wondering if it is possible to ask for more details that could be shared with me (safely via =S= box).

1- DCO screen shots illustrating (only for not sync'ed devices):

 a- Start & End devices, that are associated (and please confirm that they are associated)

 b- Synchronization of the ETL devices (In Planning Device Association mode, -> ETL Integration, right click on the etl device(s) and then select 'Synchronize external data')

2- DCO server logs (can be downloaded from webmin interface -> Struxure DC Operation > Download Log Files > Download log files)

3- DCO backup file

I will send you an invite to my =S= box shortly so the data (if possible) can share safely with me, thanks.

By the way, I was wondering if this ETL job is developed & implemented by =S= ?

Kind regards

(CID:126175361)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 01:41 AM . Last Modified: ‎2024-04-05 04:03 AM

In response to DCIM_Support
0 Likes
0
1640
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 01:41 AM . Last Modified: ‎2024-04-05 04:03 AM

We decided to recreate the import database by removing it>creating a new one>re-associating the devices.

It would be nice to know the root cause, and the logs might hold the clue; however, we decided to the timeliest solution is to just "recreate" it. We'll be forced to take a more in-depth look at it if it happens again.

Thank again

(CID:126176663)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 01:41 AM . Last Modified: ‎2024-04-05 04:03 AM

In response to DCIM_Support
0 Likes
0
1640
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 01:41 AM . Last Modified: ‎2024-04-05 04:03 AM

Hi Thomas,

Okay, many thanks for the update.

Kind regards

(CID:126177071)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 01:41 AM . Last Modified: ‎2024-04-05 04:03 AM

0 Likes
0
1640
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 01:41 AM . Last Modified: ‎2024-04-05 04:03 AM

Hi Ed,

We are using version: 8.0.3-66536-08cb94

(CID:126173504)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 01:41 AM . Last Modified: ‎2024-04-05 04:03 AM

0 Likes
0
1640
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 01:41 AM . Last Modified: ‎2024-04-05 04:03 AM

It appears that only the "public_network_connection" table has stopped working. I actually changed the "state_flag" column value to "changed" for ALL of the records in the "public_port_configuration" table, and 98% changed back to "synced."

(CID:126173515)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 01:41 AM . Last Modified: ‎2023-10-22 09:35 PM

0 Likes
0
1640
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 01:41 AM . Last Modified: ‎2023-10-22 09:35 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore