Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

problem adding netbotz 250 in Ecostruxure IT

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • problem adding netbotz 250 in Ecostruxure IT
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
160
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
cristian
cristian Explorer
Explorer

Posted: ‎2020-07-31 07:47 AM

0 Likes
3
3003
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-31 07:47 AM

problem adding netbotz 250 in Ecostruxure IT

Hello team,

 

we have a customer that is trying to add his netbotz 250 in the ecostruxure IT, we could put the IP address to the netbotz and see it by web browser, the netbotz do correct ping too, but when we try to add the ip to the ecostruxure it the software doesnt recognice the netbotz.

 

We checked with the customer the followings items:

 

• Connect the netbozt directly to the PC's network card .. both on the same IP address and mask

• The internet output of that pc was made by wifi.

• ... the localhost detects connectivity ... and ping the netbotz responds ... but Ecostruxure does not detect it

• they have no policies ... nor hardware in between ...

• And I have disabled the firewall of w10.

 

they have windows 10.

 

i attached a video showing the problem.

 

could you help us with this?

 

thanks in advance.

 

 

Attachments
video.mp4
Labels
  • Labels:
  • IT Expert
  • NetBotz
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
APC_Steve
APC_Steve Leader
Leader

Posted: ‎2020-07-31 07:51 AM

0 Likes
2
2997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-31 07:51 AM

Hi @cristian ,

 

Please make sure you've verified the SNMP credentials on the 250 and that they match what's in the software. New NMC based products come with new firmware that disables SNMP by default. You must actually log into the device and enable the correct version of SNMP as well as adding the proper community names or passphrases.

 

Thanks,

Steve

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

cristian
cristian Explorer
Explorer

Posted: ‎2020-07-31 08:00 AM

In response to APC_Steve
0 Likes
1
2995
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-31 08:00 AM

Hello Steve, thanks for the answer,

 

what you mean with "well as adding the proper community names or passphrases." where i add this?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

APC_Steve
APC_Steve Leader
Leader

Posted: ‎2020-07-31 08:17 AM

In response to cristian
1 Like
0
2988
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-31 08:17 AM

Hi @cristian ,

 

I can't speak for IT advisor. For the 250 though, assuming you're using SNMP version 1. Enable it:

image.png

---------------------

 

Then enter the community names and limit IPs that can access it. I suggest leaving it open (all 0s) for testing. Go to access control:
image.png

 

Then configure or validate the community names:

image.png

 

They may be blank to start with so you'll have to know what's set up in the IT Advisor software. Again, I am not familiar with the settings in the software but your video shows a good place to start:

image.png

 

 

If you're still having issues after that, you may want to troubleshoot SNMP. The following k-base may be of some help:

http://www.apc.com/us/en/faqs/FA226273

 

Please note that although this does mention troubleshooting for DCE, the general troubleshooting principals are the same.


Steve

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore