Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

netbotz 750 output relays

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase โ†’ Use quotes " " (e.g., "error 404")
  • Wildcard โ†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR โ†’ Combine keywords (e.g., login AND error, login OR signโ€‘in)
  • Keep it short โ†’ Use 2โ€“3 relevant words , not full sentences
  • Filters โ†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Re: netbotz 750 output relays
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
160
Jef
Jef Leader
114
gsterling
gsterling Mentor
79
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
Gabi
Gabi
Mentor

Posted: โ€Ž2024-05-10 09:19 AM

1 Like
4
3779
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2024-05-10 09:19 AM

netbotz 750 output relays

Hello all,

 

I tried to configure for certain alarms the two output relays to activate and when the alarm disappears, the relay to return to the deactivated state, but it seems that the relays only receive the command when the alarm is generated and when the alarm is canceled, the relays do not change the state back as would be normal

the version is 5.3.5 and I tried it on two pieces of equipment with the same result and the relays are the ones included in the equipment, not the ones connected to the universal sensons ports

Has anyone encountered this problem?

 

thanks

Labels
  • Labels:
  • NetBotz
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Cory_McDonald
Cory_McDonald Champion
Champion

Posted: โ€Ž2024-05-13 05:17 AM

0 Likes
0
3713
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2024-05-13 05:17 AM

Hi @Gabi,

 

The relays should go to abnormal state when an alarm occurs, and go back to a normal state when the alarm resolves.  If the alarm is active at the time that you performed the alarm configuration for the output relays, the action configuration likely will not take place until it is resolved and then occurs again.

 

If you can provide step by step details as to your testing, including the results after each test and images of the configuration it may help the community better assist you.

 

Regards,

Cory

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Cory_McDonald
Cory_McDonald Champion
Champion

Posted: โ€Ž2024-05-13 05:17 AM

0 Likes
0
3713
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2024-05-13 05:17 AM

Hi @Gabi,

 

The relays should go to abnormal state when an alarm occurs, and go back to a normal state when the alarm resolves.  If the alarm is active at the time that you performed the alarm configuration for the output relays, the action configuration likely will not take place until it is resolved and then occurs again.

 

If you can provide step by step details as to your testing, including the results after each test and images of the configuration it may help the community better assist you.

 

Regards,

Cory

Reply

Link copied. Please paste this link to share this article on your social media post.

Gabi
Gabi
Mentor

Posted: โ€Ž2024-05-13 11:50 PM

0 Likes
0
3696
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2024-05-13 11:50 PM

Hello Cory,

 

attached screens with the setup..... the setup steps are pretty intuitive so I can't figure out how to configure it wrong ๐Ÿ˜

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Gabi
Gabi
Mentor

Posted: โ€Ž2024-05-14 01:20 AM

1 Like
1
3694
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2024-05-14 01:20 AM

hmmm...strange.....after I tortured it a few times it started to work......I hope it will also work on the production netbotz, because this was a test

Reply

Link copied. Please paste this link to share this article on your social media post.

Cory_McDonald
Cory_McDonald Champion
Champion

Posted: โ€Ž2024-08-21 07:48 AM

In response to Gabi
0 Likes
0
3436
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2024-08-21 07:48 AM

Hi @Gabi,

 

Were you able to get this to work on your production appliance?  Just wanted to follow-up on this issue.

 

Regards,

Cory

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 

Youโ€™ve reached the end of your document

WHATโ€™S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore