Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

link 150 oid / mib files

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Re: link 150 oid / mib files
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-03-03 06:18 AM

0 Likes
2
2889
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-03 06:18 AM

link 150 oid / mib files

Hi,

 

I'm in IT so don't really know what i'm talking about re this electric gear to warn you!

 

Basically we have an ethernet gateway link 150 meter.  with other meters in our business we can get the oid number from the mib library to read the meter using our prtg snmp monitoring software.

 

Is it possible to get the oid/mib files for a link 150?

 

If not is the only way to read the power usage to get the v expensive schneider software?

 

Any help / pointers appreciated.

 

Thanks

Labels
  • Labels:
  • power monitoring expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
APC_Steve
APC_Steve Leader
Leader

Posted: ‎2021-03-03 06:28 AM . Last Modified: ‎2021-03-03 06:29 AM

0 Likes
1
2885
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-03 06:28 AM . Last Modified: ‎2021-03-03 06:29 AM

Hi @Anonymous user ,

 

If you're using this:

https://www.se.com/ww/en/product/EGX150/link-150---ethernet-gateway---2-ethernetport---24-v-dc-and-p...

 

What you're likely doing is connecting a modbus device on one side and network on the other..

If this is the case, polling the 150 using SNMP will only provide you a little info on the gateway itself and not the connected devices. What this is designed for is to translate Modbus RTU (serial) to modbus over IP. 

To monitor the devices through this gateway, you would poll the IP and secondary device(s) using modbus over IP and not using SNMP. The modbus register map would be that of the devices and not specific to the gateway.

 

Thanks,

Steve

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
APC_Steve
APC_Steve Leader
Leader

Posted: ‎2021-03-03 06:28 AM . Last Modified: ‎2021-03-03 06:29 AM

0 Likes
1
2886
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-03 06:28 AM . Last Modified: ‎2021-03-03 06:29 AM

Hi @Anonymous user ,

 

If you're using this:

https://www.se.com/ww/en/product/EGX150/link-150---ethernet-gateway---2-ethernetport---24-v-dc-and-p...

 

What you're likely doing is connecting a modbus device on one side and network on the other..

If this is the case, polling the 150 using SNMP will only provide you a little info on the gateway itself and not the connected devices. What this is designed for is to translate Modbus RTU (serial) to modbus over IP. 

To monitor the devices through this gateway, you would poll the IP and secondary device(s) using modbus over IP and not using SNMP. The modbus register map would be that of the devices and not specific to the gateway.

 

Thanks,

Steve

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-03-03 06:50 AM

In response to APC_Steve
0 Likes
0
2880
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-03 06:50 AM

perfect thats a lot clearer thank you

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore