Ask our Experts
Didn't find what you are looking for? Ask our experts!
New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Search in
Please select a country to continue with beta search.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 01:06 PM . Last Modified: 2024-04-04 12:39 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 01:07 PM . Last Modified: 2024-04-04 12:38 AM
Hello Enric. Please refer to this note.
The DCIM Asset Entitlement website is temporarily unavailable
The dcimassets site is temporarily offline due to maintenance. Please contact your tech support team if licenses are needed.
Regards
Greg Sterling
(CID:134686999)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 01:07 PM . Last Modified: 2024-04-04 12:38 AM
thanks Greg, I can wait
Regards,
Enric
(CID:134687004)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 01:07 PM . Last Modified: 2024-04-04 12:38 AM
Hello Enric. The dcimassets portal should be open to customers now.
Regards
Greg Sterling
(CID:137727742)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 01:07 PM . Last Modified: 2023-10-22 04:30 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.