Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

connectivity issues with the Wireless Temperature sensors.

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • connectivity issues with the Wireless Temperature sensors.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 05:26 PM . Last Modified: ‎2024-04-03 03:22 AM

0 Likes
6
2522
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 05:26 PM . Last Modified: ‎2024-04-03 03:22 AM

connectivity issues with the Wireless Temperature sensors.

I am consistently getting alerts that the sensors are unplugged or have malfunctioned, and have to constantly reboot the sensors. sometimes the sensors will come back online after rebooting and sometimes I have to place them directly on the Rack monitor for it to pick the sensor back up. The RSSI strength is high enough that I don't believe they should just be dropping off like this. We have a large amount of these sensors deployed and need to find out what is causing this. Has anyone had this issue and found a solution?

(CID:140220062)

Labels
  • Labels:
  • Data Center Expert
  • NetBotz
  • Tags:
  • bug
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 05:26 PM . Last Modified: ‎2024-04-03 03:22 AM

0 Likes
0
2522
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 05:26 PM . Last Modified: ‎2024-04-03 03:22 AM

I also wanted to mention that all of the sensors have been updated the the latest firmware.

(CID:140220064)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 05:26 PM . Last Modified: ‎2024-04-03 03:22 AM

0 Likes
2
2522
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 05:26 PM . Last Modified: ‎2024-04-03 03:22 AM

Hi Matthew,

What exactly is the RSSI? I would suggest in issues like this that you keep it above 50. Also, if you have the coordinator plugged into the appliance itself, you may want to connect it to a USB extension or if not on a 250, a usb repeater cable. Which appliance is it and what firmware is it running? I know you said the sensors are at the latest but can you provide the version number? 

Id also be curious to know if it happens at a specific time. For instance if it’s happening during work hours and not off hours, it may be some sort of interference. Is there any fiber running near the sensors with the issues?  Is it all sensors or just some?

 

steve. 

(CID:140220172)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 05:26 PM . Last Modified: ‎2024-04-03 03:22 AM

In response to DCIM_Support
0 Likes
0
2521
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 05:26 PM . Last Modified: ‎2024-04-03 03:22 AM

Hi Steve, The RSSI's are ranging anywhere from 75% to 98% so I do not believe this is the issue. We have 660 sensors spread across 22 NetBotz570 Rack monitor devices. Does the USB extension apply to a Rack monitor 570? The firmware version on the Sensors is 1.1.2, and the firmware on the Coordinators is 1.1.1. The Rack monitor is running OS version 4.6.3. The timing seems random and when I restart one and get it back online another one will fall off so it seems like it can happen to any sensor. As far as fiber goes. there is fiber in the cage but I would not say it is 'near' the sensors. Most of it is ran above the rack on a ladder tray.

(CID:140707823)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 05:26 PM . Last Modified: ‎2024-04-03 03:22 AM

In response to DCIM_Support
0 Likes
0
2522
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 05:26 PM . Last Modified: ‎2024-04-03 03:22 AM

Hi Matthew,

If RSSI can be seen over time at a consistent 75%, there would appear to be no issue there. I would't worry about any issues until it regularly went below 50%. The warning for this threshold is (I believe) around 30 but I like to troubleshoot with better numbers. I'm assuming your battery voltage is fine?

With the NetBotz 570 being mounted in a rack, a USB extender is usually a good idea. I normally suggest this with RSSI issues but you don't seem to have those kinds of issues. The 570 can use an extender or a USB repeater (basically a 1 port hub). the 250 can not use the repeater as it does not have the driver for it.

660 sensors is a lot of sensors. Are they all installed within close range with each other? Are you using any of the coordinators as USB routers? These can add extra traffic to the already busy wireless networks. 

I'd also be curious to know if you've turned off any settings for auto-join or if you had used that feature at all. If your NetBotz are in close enough proximity so that they would be able to communicate with sensors associated to other networks, I could see where the sensor could be discovered by multiple networks during a comm lost issue and could start communicating with other NetBotz. You'd have to verify the commission  lists of nearby appliances to verify that.

 

Steve

(CID:140708316)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 05:26 PM . Last Modified: ‎2024-04-03 03:21 AM

0 Likes
0
2522
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 05:26 PM . Last Modified: ‎2024-04-03 03:21 AM

Hey Guys,

Even i am facing the same issue. we have about 280 of these T/H sensors. For every 40 sensor we have one netbotz 250 controlling it. Randomly the sensors get inactive/unplugged and sometimes we have to restart the sensor.

Thanks

(CID:140707575)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 05:26 PM . Last Modified: ‎2023-10-22 04:28 AM

0 Likes
0
2522
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 05:26 PM . Last Modified: ‎2023-10-22 04:28 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore