Posted: 2020-07-03 05:01 PM . Last Modified: 2024-04-08 12:21 AM
The NMC is V3.7.2 and I would like to upgrade card. When I select upgrades and apply upgrade the device doesn't show on the device update list. The UPS is a smart-ups 3000XL
(CID:120133142)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 05:02 PM . Last Modified: 2024-04-08 12:20 AM
Hi Jan,
The SUMX app or the Smart-UPS / Matrix application is the most recent available NMC1 (AP9617/18/19) for the Smart-UPS in the StruxureWare DCE firmware catalog. I just downloaded the most recent and checked:

6.4.6 firmware is only available for the NMC2 cards (AP9630/31/35).
If there is a newer version, it may take a little time to get it into the catalog but until that is done, the only option would be to manually upgrade the cards. At this time however, that seems to be the most current available on the downloads page:

Thanks,
Steve
(CID:120133154)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 05:02 PM . Last Modified: 2024-04-08 12:20 AM
Hi Jan,
The SUMX app or the Smart-UPS / Matrix application is the most recent available NMC1 (AP9617/18/19) for the Smart-UPS in the StruxureWare DCE firmware catalog. I just downloaded the most recent and checked:

6.4.6 firmware is only available for the NMC2 cards (AP9630/31/35).
If there is a newer version, it may take a little time to get it into the catalog but until that is done, the only option would be to manually upgrade the cards. At this time however, that seems to be the most current available on the downloads page:

Thanks,
Steve
(CID:120133154)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 05:02 PM . Last Modified: 2024-04-08 12:20 AM
Thanks Steve
(CID:120135675)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 05:02 PM . Last Modified: 2023-10-22 04:21 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.