Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

We are getting the folowing on our twenty-nine (29) UPS'S:

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase โ†’ Use quotes " " (e.g., "error 404")
  • Wildcard โ†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR โ†’ Combine keywords (e.g., login AND error, login OR signโ€‘in)
  • Keep it short โ†’ Use 2โ€“3 relevant words , not full sentences
  • Filters โ†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Re: We are getting the folowing on our twenty-nine (29) UPS'S:
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
160
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-04 11:55 PM . Last Modified: โ€Ž2024-04-04 01:16 AM

0 Likes
18
2400
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 11:55 PM . Last Modified: โ€Ž2024-04-04 01:16 AM

We are getting the folowing on our twenty-nine (29) UPS'S:

(CID:134034671)

Labels
  • Labels:
  • IT Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 18
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-04 11:55 PM . Last Modified: โ€Ž2024-04-04 01:16 AM

0 Likes
0
2401
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 11:55 PM . Last Modified: โ€Ž2024-04-04 01:16 AM

The Gateway is up and running and it is communicating with the EcoStruxure IT Digital Service as follows:

 

(CID:134034685)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-04 11:55 PM . Last Modified: โ€Ž2024-04-04 01:16 AM

0 Likes
0
2399
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 11:55 PM . Last Modified: โ€Ž2024-04-04 01:16 AM

Dear John Beck,

In this case, a reliable communication between your gateway and your UPS's is important.

Does your gateway's web-GUI have alarms?

What is the status of the communication between your gateway and the above-mentioned UPS?

With respect.

(CID:134034704)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-04 11:55 PM . Last Modified: โ€Ž2024-04-04 01:15 AM

0 Likes
0
2400
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 11:55 PM . Last Modified: โ€Ž2024-04-04 01:15 AM

Yes the Gateway has "not responding" alarms for all twenty-nine (29) UPS's. I just posted one (for UPS M1911UP1) as a representative example.

(CID:134034710)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-04 11:55 PM . Last Modified: โ€Ž2024-04-04 01:15 AM

0 Likes
0
2399
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 11:55 PM . Last Modified: โ€Ž2024-04-04 01:15 AM

Ok, then what is the essence of your question, please tell us ๐Ÿ˜€.

You have an unreliable communication between your gateway and the UPS's.

Have you installed the gateway software on an server as required by the EcoStruxure IT Gateway system requirements?

With respect.

(CID:134034719)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-04 11:56 PM . Last Modified: โ€Ž2024-04-04 01:15 AM

0 Likes
7
2402
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 11:56 PM . Last Modified: โ€Ž2024-04-04 01:15 AM

Dear @John Beck,

 

Please try rebooting the server that the EcoStruxure IT Gateway is installed on (or restarting the EcoStruxure IT Gateway services). Please let me know if this fixes the issue you are seeing.

 

Thanks,

Rick

(CID:134034725)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-04 11:56 PM . Last Modified: โ€Ž2024-04-04 01:15 AM

In response to DCIM_Support
0 Likes
0
2402
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 11:56 PM . Last Modified: โ€Ž2024-04-04 01:15 AM

The EcoStruxure IT Gateway is currently installed on my Laptop. We have a request that is being processed from our Server Group to provide us with a Virtual Machine (VM) to put the EcoStruxure IT Gateway System on.

(CID:134034731)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-04 11:56 PM . Last Modified: โ€Ž2024-04-04 01:15 AM

In response to DCIM_Support
0 Likes
0
2402
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 11:56 PM . Last Modified: โ€Ž2024-04-04 01:15 AM

If you restart the EcoStruxure IT Gateway service your devices will come back online.

 

-Rick

(CID:134034742)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-04 11:56 PM . Last Modified: โ€Ž2024-04-04 01:15 AM

In response to DCIM_Support
0 Likes
0
2402
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 11:56 PM . Last Modified: โ€Ž2024-04-04 01:15 AM

Rick,

 

How do I restart the EcoStruxure IT Gateway Service?

(CID:134034758)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-04 11:56 PM . Last Modified: โ€Ž2024-04-04 01:15 AM

In response to DCIM_Support
0 Likes
0
2402
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 11:56 PM . Last Modified: โ€Ž2024-04-04 01:15 AM

  1. Go to Control Panel > Administrative Tools > Services.
  2. Restart the EcoStruxure IT Gateway Server service.

(CID:134034763)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-04 11:56 PM . Last Modified: โ€Ž2024-04-04 01:15 AM

In response to DCIM_Support
0 Likes
0
2402
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 11:56 PM . Last Modified: โ€Ž2024-04-04 01:15 AM

I can't believe I asked how to restart a service. I should have known that. I feel like an idiot now.

(CID:134034771)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-04 11:56 PM . Last Modified: โ€Ž2024-04-04 01:15 AM

In response to DCIM_Support
0 Likes
0
2402
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 11:56 PM . Last Modified: โ€Ž2024-04-04 01:15 AM

Thank you for your help Rick.

(CID:134034776)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-04 11:56 PM . Last Modified: โ€Ž2024-04-04 01:15 AM

In response to DCIM_Support
0 Likes
0
2402
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 11:56 PM . Last Modified: โ€Ž2024-04-04 01:15 AM

๐Ÿ˜€ It's all good. Just took a look at all your devices and it looks like we are back in business?

(CID:134034778)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-04 11:57 PM . Last Modified: โ€Ž2024-04-04 01:15 AM

0 Likes
1
2402
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 11:57 PM . Last Modified: โ€Ž2024-04-04 01:15 AM

Yes it does seem that we have unreliable communication between the gateway and the UPS's.  We have a request for a Virtual Machine (VM) to put the EcoStruxure IT Gateway System on. That should provide more robust communication between the Gateway and the UPS's. In the meantime, meaning right now - do you know of any way that I can get the communication back via either the EcoStruxure IT App or the EcoStruxure IT Gateway?

(CID:134034727)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-04 11:57 PM . Last Modified: โ€Ž2024-04-04 01:15 AM

In response to DCIM_Support
0 Likes
0
2402
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 11:57 PM . Last Modified: โ€Ž2024-04-04 01:15 AM

Dear John Beck,

From your question:

...In the meantime, meaning right now - do you know of any way that I can get the communication back via either the EcoStruxure IT App or the EcoStruxure IT Gateway?

I know that you installed the gateway software on your work laptop just to try. Of course you can restart your laptop, but it seems to me that the problem is not only in communication, but also in insufficient computing power.

With respect.

(CID:134034736)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-04 11:57 PM . Last Modified: โ€Ž2024-04-04 01:15 AM

0 Likes
0
2402
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 11:57 PM . Last Modified: โ€Ž2024-04-04 01:15 AM

  1. are all of the UPSs on the same L2 subnet?
  2. if on the same subnet, are they all connected to the same physical switch?
  3. are all of your UPSs having the same problem? - you say "on OUR 29 UPSs" ....
  4. what code is running on these UPSs ?
  5. what model network card is in these UPSs ?

 

I'm not running this Ecostruxure IT Gateway thing, but I've seen unreliable communication from several UPSs - when the network is operating without issue. Haven't figured the root cause out yet.

 

(CID:134034750)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-04 11:57 PM . Last Modified: โ€Ž2024-04-04 01:15 AM

0 Likes
0
2402
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 11:57 PM . Last Modified: โ€Ž2024-04-04 01:15 AM

Yes, all twenty-nine (29) UPS's are back online and responding.

(CID:134036168)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-04 11:57 PM . Last Modified: โ€Ž2024-04-04 01:15 AM

0 Likes
0
2402
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 11:57 PM . Last Modified: โ€Ž2024-04-04 01:15 AM

Dear John Beck,

Tell us, please, did you solve your problem or not?

With respect.

(CID:134679983)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-04 11:57 PM . Last Modified: โ€Ž2023-10-22 04:16 AM

0 Likes
0
2401
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 11:57 PM . Last Modified: โ€Ž2023-10-22 04:16 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

Youโ€™ve reached the end of your document

WHATโ€™S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore