Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Tripp lite UPS contains no device alarms

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Re: Tripp lite UPS contains no device alarms
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:20 AM . Last Modified: ‎2024-04-02 11:36 PM

0 Likes
12
3660
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:20 AM . Last Modified: ‎2024-04-02 11:36 PM

Tripp lite UPS contains no device alarms

Hi, I'm trying to get some Tripp Lite UPS to alarm to Struxureware. Struxureware discovers the UPS and I can view device sensors. I downloaded the most recent Tripp Lite UPS DDF (version 6) and TrippLite WEBCARDLX DDF (version 7). I go to Alarm Configuration and select a UPS and get "UPS - contains no device alarms" (the ip address is correct). How do I tell Struxureware to use the DDF for this UPS? Struxureware version 7.2.2.76

(CID:153092111)

Labels
  • Labels:
  • Data Center Expert
  • DDF
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:20 AM . Last Modified: ‎2024-04-02 11:36 PM

0 Likes
0
3660
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:20 AM . Last Modified: ‎2024-04-02 11:36 PM

Dear Paul O,

Since you are connecting 3rd party UPS to DCE software, first I highly recommend updating your UPS MIB DDF-file. You have a very old version of DCE-7.2.2 with an outdated version of UPS MIB v.4. The latest version of the UPS MIB v.11 DDF-file can be downloaded from the DDF resource, for example, like this:

Additionally, check again that you are using the correct and latest DDF-files for your Tripp Lite UPS.

In addition, I highly recommend that you take the time to upgrade your DCE software to the latest version of DCE-7.8.0. Since older versions of DCE software may no longer be supported when contacting to =SE= technical support.

In addition, you may find these two similar topics useful:  and I am testing Tripp-Lite UPS unit compatibility with Struxureware software and found that Struxureware is not able to report any information, critical alarms from Tripp-Lite UPS unit in short or details email alert.

With respect.

(CID:153092328)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 12
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:20 AM . Last Modified: ‎2024-04-02 11:36 PM

0 Likes
0
3660
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:20 AM . Last Modified: ‎2024-04-02 11:36 PM

Dear Paul O,

Can you show a couple of screenshots from DCE-client, please? And then they will help you faster and better 😀.

With respect.

(CID:153092162)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:20 AM . Last Modified: ‎2024-04-02 11:36 PM

0 Likes
0
3660
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:20 AM . Last Modified: ‎2024-04-02 11:36 PM

Here is the DFF files we have on the server:

Here is a device running the older TrippLite websnmpcard:

 

Here is what we get on a device running the newer WEBCARDLX:

Mix of WEBCARDLX and websnmpcards and various Tripp-Lite models. WEBCARDLX version 15.5.2, websnmpcard version 12.06.0069. 

Please let me know what other information might be helpful.

(CID:153092306)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:20 AM . Last Modified: ‎2024-04-02 11:36 PM

0 Likes
0
3661
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:20 AM . Last Modified: ‎2024-04-02 11:36 PM

Dear Paul O,

Since you are connecting 3rd party UPS to DCE software, first I highly recommend updating your UPS MIB DDF-file. You have a very old version of DCE-7.2.2 with an outdated version of UPS MIB v.4. The latest version of the UPS MIB v.11 DDF-file can be downloaded from the DDF resource, for example, like this:

Additionally, check again that you are using the correct and latest DDF-files for your Tripp Lite UPS.

In addition, I highly recommend that you take the time to upgrade your DCE software to the latest version of DCE-7.8.0. Since older versions of DCE software may no longer be supported when contacting to =SE= technical support.

In addition, you may find these two similar topics useful:  and I am testing Tripp-Lite UPS unit compatibility with Struxureware software and found that Struxureware is not able to report any information, critical alarms from Tripp-Lite UPS unit in short or details email alert.

With respect.

(CID:153092328)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:20 AM . Last Modified: ‎2024-04-02 11:36 PM

0 Likes
1
3660
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:20 AM . Last Modified: ‎2024-04-02 11:36 PM

Thank you for the information. I updated to the latest UPS MIB and nothing changed. I just downloaded the TrippLite DDF's yesterday so I assume they are the latest. We are in the process of upgrading the DCE. I guess I'll wait for that to be done and then see if anything changes. Thanks for your help.

(CID:153092348)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:20 AM . Last Modified: ‎2024-04-02 11:36 PM

In response to DCIM_Support
0 Likes
0
3660
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:20 AM . Last Modified: ‎2024-04-02 11:36 PM

From your question:

Mix of WEBCARDLX and websnmpcards and various Tripp-Lite models. WEBCARDLX version 15.5.2, websnmpcard version 12.06.0069.

I recommend using only the WEBCARDLX DDF-file and the DDF-file for your UPS (in total, there should be only two DDF-files for Tripp-Lite in DCE software).

With respect.

(CID:153092356)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:20 AM . Last Modified: ‎2024-04-02 11:36 PM

0 Likes
1
3660
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:20 AM . Last Modified: ‎2024-04-02 11:36 PM

Sorry, I forgot to mention I did check those two articles you linked. The second one especially because that person is getting much more out of Alarm Configuration than I am, but, it could be because his version of DCE is newer.

(CID:153092354)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:21 AM . Last Modified: ‎2024-04-02 11:36 PM

In response to DCIM_Support
0 Likes
0
3660
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:21 AM . Last Modified: ‎2024-04-02 11:36 PM

Ok, let us know the result of your upgrade, please.

 

(CID:153092358)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:21 AM . Last Modified: ‎2024-04-02 11:36 PM

0 Likes
1
3660
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:21 AM . Last Modified: ‎2024-04-02 11:36 PM

Correction, updated the UPS MIB did make a difference. I restarted DCE and waited a bit and now I see many more alarm options. I'll test them later today and see if it works and report back.

(CID:153092359)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:21 AM . Last Modified: ‎2024-04-02 11:36 PM

In response to DCIM_Support
0 Likes
0
3660
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:21 AM . Last Modified: ‎2024-04-02 11:36 PM

So it should be with the latest version of UPS MIB - this is important.

But it was possible not to restart the DCE-server, but simply to rediscover your UPS device in DCE-client.

With respect.

(CID:153092364)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:21 AM . Last Modified: ‎2024-04-02 11:36 PM

0 Likes
1
3660
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:21 AM . Last Modified: ‎2024-04-02 11:36 PM

Hello. For reference if anyone else finds this. Updating to UPS MIB v.11 seems to have fixed my issue, thank you very much for your assistance.

(CID:153092372)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:21 AM . Last Modified: ‎2024-04-02 11:36 PM

In response to DCIM_Support
0 Likes
0
3660
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:21 AM . Last Modified: ‎2024-04-02 11:36 PM

Ok, very thanks for the good feedback 😀.

(CID:153092382)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:21 AM . Last Modified: ‎2023-10-22 04:07 AM

0 Likes
0
3660
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:21 AM . Last Modified: ‎2023-10-22 04:07 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore