We have some temperature alerts reports but looks like the Temperature Sensors need calibrating or resetting, how do we do this i.e. our readings compared to landlords not same off by 2 to 3 celsius
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-06-08 08:34 AM
Hello @nicholas.r,
Data Center Expert monitors devices that would be reporting the temperature sensors. There would be no calibration to do on the DCE side. What model device and temperature sensor are experiencing this issue?
Regards,
Cory
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-06-09 02:23 AM
Sensors we use are the below
APC Temperature Sensor / Part Number : FEAP9335T / Manufacturer No: AP9335T
Some are also Humidity Sensors
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-06-09 10:20 AM
The AP9335T/TH do not have a calibration. For Example, when in use with a NetBotz 250A, they should have an accuracy of ±1 ºC. This specification can be found within the NetBotz 250 users guide. Usually when the sensor is only off by a few degrees, it is usually differing airflows within the environment compared to the locations of the other sensors.
From my experience, usually these differing values is due to placement within the datacenter, room, or racks. As a stabilized test, you may be able to place the sensor within a stabilized environment, such as a box or clear container (if you must see the display on the other sensor) to compare the readings and see where they both stabilize.
You can reach out to technical support also to look into any other options. They may be able to provide assistance with troubleshooting further and looking into any warranty options if the sensors are determined to be faulty.