New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Tap-Off Units Meters - Billing System
EcoStruxure IT Forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-08-1201:00 AM. Last Modified: 2026-08-1201:29 AM
Tap-Off Units Meters - Billing System
Dear Team,
Have anyone tried to connect the billing system from SE-PME [ Schneider power monitoring expert ] to ITA ? As the Tap-Off units Meters of the racks will be connected to PME and it will generate billing reports. My question is : Can ITA import this billing and show it to the the data center tenants ? and see his consumbtion \ bill via a report ?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-08-1303:42 AM
Hello TechWhiz123
I have not heard of a case where PME's billing system was integrated to ITA. You may receive a response from another Schneider resource who knows otherwise.
I know for certain there are customers who have linked PME to ITA to share power measurements from PME to ITA. This was typically meant to enrich the measurement data ITA uses for capacity planning and so on.
ITA has a set of Energy Cost reports which is a per rack "billing" report for a time period based specifically on power measurement data at the rack or the breakers feeding the racks. So if ITA is enriched with PME power data then those reports could provide a form of billing as long as the billing is strictly limited to rack based power measurements.
If you have a need to integration PME's billing system with ITA, it may be necessary to engage a solution architect from schneider to identify whether the integration itself is possible or whether a billing report can be developed through a custom service.