StructureWare data center expert 7.2.0 - how to set email escalation at 05 different levels?

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • StructureWare data center expert 7.2.0 - how to set email escalation at 05 different levels?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:37 AM . Last Modified: ‎2024-04-08 03:28 AM

0 Likes
4
2097
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:37 AM . Last Modified: ‎2024-04-08 03:28 AM

StructureWare data center expert 7.2.0 - how to set email escalation at 05 different levels?

Dear Team,

Following is the requirements of our customer for email escalation through StructureWare Data Center Expert:

1st Escalation:-
Email generate to Branch operation manager after 10 min at following conditions:

a) Power Failure

b) voltage range out (< 180v to 250v >)

c) Frequency (< 45 to 55 >)
 
2nd Escalation:-
At the time of battery backup remains 30 min email generate to Operation Manager,  Branch Manager & concern Regional Managers

3rd Escalation:-
At the time of ups failure & ATM shut down due to UPS issue email generate to concern Operation Manager, ups vender & helpdesk
 
4th Escalation:-
After 4 hrs. if the 3rd escalation not attending immediately call generate to Mr.X
 
5th Escalation:-
If the 4th one not attending the complaint after 8 hrs. email generate to Mr.Y

Please note that Mr.X & Mr.Y are setting in head office of the Bank & at escalation level 1,2, & 3 we have to send email at branch level.

We need your support to define above email escalation as per advised levels.

Please advice the steps to define all above escalation levels.
 

Best regards,
Nadeem Ansari

 

(CID:110012510)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:37 AM . Last Modified: ‎2024-04-08 03:28 AM

0 Likes
2
2097
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:37 AM . Last Modified: ‎2024-04-08 03:28 AM

Dear Nadeem,

You will need to create 5 Levels of Escalations-Alert Action in DCE software under Alarm Configuration–>Alert Action to send out an email alert for the Devices Alarms & Customized Thresholds. I would suggest you to create the Customer thresholds depending upon the product model, make of the UPS for the below parameters in DCE software.

a) Power Failure

b) voltage range out (< 180v to 250v >)

c) Frequency (< 45 to 55 >)

d) battery time remaining 30 minutes

Please find the procedure to create the Alert Action or 5 Levels of Escalations Alert Action and Procedure for associating the Alert Actions to the Notification Policy. 

Managing Alarm Actions

1) Alarm Configuration Menu > Manage Alarm Actions.

2) On the screen will be displayed the list of alarm actions that are currently defined on the system.  This screen will allow you to: Create, Edit, Delete, & Test alarm actions.  

NOTE: Actions that are listed here does not mean that they are configured to occur on an alert.  Please see section below titled "Managing Notification Policies."

3) In this example, we will create an alarm action to send an email.

  • Select Create...
  • Send E-mail > Next.
  • Fill out E-mail Action Name with something descriptive.
  • Within the E-mail section select "Add..."

In your case, you will need to set the delay of 10 minutes for the 1st level escalation, and ensure that the customized thresholds are associated to the DCE notification policy. 

  • Enter the email address you would like to send email notifications to and select OK.
    NOTE: if you have multiple, please repeat the last two steps.
  • Other options are available to set such as notification severities and scheduling.
  • Select Finish and your alarm action has been created.  To verify that it works, you can test the alarm action by clicking on it in the list and then selecting "Test..."

NOTE: At this point the alarm action has been created, but nothing will be done with it yet.  Please proceed to the Managing Notification Policies section.

Managing Notification Policies

Notification policies are where you define what actions you want to take place for device level alerts and thresholds.

NOTE: When a device is added into DCE, it will automatically be added into the default notification policy.  The default policy can't be deleted, but i can be renamed.

For this example, a new notification policy is going to be created.

1) Navigate into the Alarm Configuration Perspective and you will see your notification policies in the lower left-hand corner.

2) Select the green plus symbol in the upper right-hand corner on the Notification Policies pane to create a new notification policy.  

NOTE: If you need to edit one, you can select the notification policy and then select the edit option to the right of the green plus symbol.

3) Provide the policy with a descriptive name.

4) Select Add within the right hand side of the Actions section to add in an alarm action.  Check the check box for the alarm action that you would like to add to this policy.  You can Manage alarm action and it will bring you to the same pop-up that was used to create the alarm action above.  You can define, within the options section: Delay, repeats, and intervals.  Select OK when finished.

5) Within the lower section will be a Threshold tab and a Devices tab.  Within these tabs you can select to chose the thresholds and devices that you want to add into this policy.

NOTE: Thresholds (Communication Status - Link Status & Custom) can be added into more than one notification policy.

NOTE: Devices can only be added into one notification policy.  If you select a device that is within another notification policy and add it into this policy, it will remove it from the previous notification policy.  Please keep this in mind when designing your notification policies.

6) Select OK when finished.

Difference Between Threshold Alarms and Device Alarms

Device Alarms: When an alarm occurs on an APC device, StruxureWare Data Center Expert should see the alarm, as long as it occurs for a long enough period of time and does not clear too quickly.  When StruxureWare DCE sees the alarm, it will look to see what Notification policy that the alarm is within and then perform the alarm actions defined within it.

Threshold Alarms:  Every SNMP/ModbusTCP device that is added into StruxureWare DCE by default will have a Communication Status - Link Status threshold.  This threshold can not be deleted, but it can be disabled.  You can also define other custom thresholds within DCE and associate them to one or more notification policies.  These custom thresholds can be based off of any sensor value that we are pulling in from a unit, whether APC or third party devices.

In the following example, the email alert will be sent out to first level email only if the Customized threshold alarm is not getting cleared within 5 minutes, and third level email alert will be sent out by DCE only if the alarm is not getting cleared within 10 minutes since alarm generation in DCE software. You can adjust the alert actions sequences based on your requirement. 

 

I hope this helps. 

Regards,

Bala

(CID:110012547)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:37 AM . Last Modified: ‎2024-04-08 03:28 AM

0 Likes
2
2098
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:37 AM . Last Modified: ‎2024-04-08 03:28 AM

Dear Nadeem,

You will need to create 5 Levels of Escalations-Alert Action in DCE software under Alarm Configuration–>Alert Action to send out an email alert for the Devices Alarms & Customized Thresholds. I would suggest you to create the Customer thresholds depending upon the product model, make of the UPS for the below parameters in DCE software.

a) Power Failure

b) voltage range out (< 180v to 250v >)

c) Frequency (< 45 to 55 >)

d) battery time remaining 30 minutes

Please find the procedure to create the Alert Action or 5 Levels of Escalations Alert Action and Procedure for associating the Alert Actions to the Notification Policy. 

Managing Alarm Actions

1) Alarm Configuration Menu > Manage Alarm Actions.

2) On the screen will be displayed the list of alarm actions that are currently defined on the system.  This screen will allow you to: Create, Edit, Delete, & Test alarm actions.  

NOTE: Actions that are listed here does not mean that they are configured to occur on an alert.  Please see section below titled "Managing Notification Policies."

3) In this example, we will create an alarm action to send an email.

  • Select Create...
  • Send E-mail > Next.
  • Fill out E-mail Action Name with something descriptive.
  • Within the E-mail section select "Add..."

In your case, you will need to set the delay of 10 minutes for the 1st level escalation, and ensure that the customized thresholds are associated to the DCE notification policy. 

  • Enter the email address you would like to send email notifications to and select OK.
    NOTE: if you have multiple, please repeat the last two steps.
  • Other options are available to set such as notification severities and scheduling.
  • Select Finish and your alarm action has been created.  To verify that it works, you can test the alarm action by clicking on it in the list and then selecting "Test..."

NOTE: At this point the alarm action has been created, but nothing will be done with it yet.  Please proceed to the Managing Notification Policies section.

Managing Notification Policies

Notification policies are where you define what actions you want to take place for device level alerts and thresholds.

NOTE: When a device is added into DCE, it will automatically be added into the default notification policy.  The default policy can't be deleted, but i can be renamed.

For this example, a new notification policy is going to be created.

1) Navigate into the Alarm Configuration Perspective and you will see your notification policies in the lower left-hand corner.

2) Select the green plus symbol in the upper right-hand corner on the Notification Policies pane to create a new notification policy.  

NOTE: If you need to edit one, you can select the notification policy and then select the edit option to the right of the green plus symbol.

3) Provide the policy with a descriptive name.

4) Select Add within the right hand side of the Actions section to add in an alarm action.  Check the check box for the alarm action that you would like to add to this policy.  You can Manage alarm action and it will bring you to the same pop-up that was used to create the alarm action above.  You can define, within the options section: Delay, repeats, and intervals.  Select OK when finished.

5) Within the lower section will be a Threshold tab and a Devices tab.  Within these tabs you can select to chose the thresholds and devices that you want to add into this policy.

NOTE: Thresholds (Communication Status - Link Status & Custom) can be added into more than one notification policy.

NOTE: Devices can only be added into one notification policy.  If you select a device that is within another notification policy and add it into this policy, it will remove it from the previous notification policy.  Please keep this in mind when designing your notification policies.

6) Select OK when finished.

Difference Between Threshold Alarms and Device Alarms

Device Alarms: When an alarm occurs on an APC device, StruxureWare Data Center Expert should see the alarm, as long as it occurs for a long enough period of time and does not clear too quickly.  When StruxureWare DCE sees the alarm, it will look to see what Notification policy that the alarm is within and then perform the alarm actions defined within it.

Threshold Alarms:  Every SNMP/ModbusTCP device that is added into StruxureWare DCE by default will have a Communication Status - Link Status threshold.  This threshold can not be deleted, but it can be disabled.  You can also define other custom thresholds within DCE and associate them to one or more notification policies.  These custom thresholds can be based off of any sensor value that we are pulling in from a unit, whether APC or third party devices.

In the following example, the email alert will be sent out to first level email only if the Customized threshold alarm is not getting cleared within 5 minutes, and third level email alert will be sent out by DCE only if the alarm is not getting cleared within 10 minutes since alarm generation in DCE software. You can adjust the alert actions sequences based on your requirement. 

 

I hope this helps. 

Regards,

Bala

(CID:110012547)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:38 AM . Last Modified: ‎2024-04-08 03:28 AM

In response to DCIM_Support
0 Likes
0
2097
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:38 AM . Last Modified: ‎2024-04-08 03:28 AM

Thanks Bala for your timely support & detail guidelines.

 

All policies are set & tested are working fine.

 

Best regards,

Nadeem Ansari

(CID:110014581)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:38 AM . Last Modified: ‎2024-04-08 03:28 AM

In response to DCIM_Support
0 Likes
0
2097
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:38 AM . Last Modified: ‎2024-04-08 03:28 AM

You are welcome Nadeem! I am glad that I could help! Have a nice day!

(CID:110014584)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:38 AM . Last Modified: ‎2023-10-22 03:58 AM

0 Likes
0
2097
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:38 AM . Last Modified: ‎2023-10-22 03:58 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore