Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Sensors showing as "Unplugged" after DCE appliance reboot.

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Sensors showing as "Unplugged" after DCE appliance reboot.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:45 PM . Last Modified: ‎2024-04-03 12:42 AM

0 Likes
5
1843
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:45 PM . Last Modified: ‎2024-04-03 12:42 AM

Sensors showing as "Unplugged" after DCE appliance reboot.

I rebooted the  DCE appliance after it started sending repeat email  for a single alarm, as documented here: https://www.schneider-electric.com/en/faqs/FA239225/

After the reboot many sensors are showing as unplugged.

The last time I saw something like this is was during an upgrade when some DDFs were changed to be more compatible with DCO.

Is it possible that DCE updated it's DDFs on reboot?


(CID:148342521)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:45 PM . Last Modified: ‎2024-04-03 12:42 AM

0 Likes
3
1842
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:45 PM . Last Modified: ‎2024-04-03 12:42 AM

Hi John,

DCE won't update it's DDFs unless you:

1: Upgrade the server.

2: Import DDFs manually.

3: Import over the internet.

 

I have seen instances where partial communications issues can cause sensors to report unplugged but the device as a whole stays on-line. If it were something like the DDF upgrade you mentioned, you should see some sensors off-line and others on-line. You would also see duplicates of the off-line sensors (or most of them).

Are all devices reporting sensor issues? If only some, are they all similar models or device types?

The issue you're speaking of with DDF updates on upgrade is also some time ago. I'm not aware of recent issues of this type except possibly with manual updates of 3rd party DDFs.

There is a possibility that there's an issue with the DDF(s) that are used to monitor the device, you could always look to update them or possibly upgrade DCE itself. If you've been running the server for 500+ days as noted in the k-base you linked, you're likely not on the most recent version.

 

Thanks,

Steve

(CID:148342532)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:45 PM . Last Modified: ‎2024-04-03 12:42 AM

0 Likes
3
1843
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:45 PM . Last Modified: ‎2024-04-03 12:42 AM

Hi John,

DCE won't update it's DDFs unless you:

1: Upgrade the server.

2: Import DDFs manually.

3: Import over the internet.

 

I have seen instances where partial communications issues can cause sensors to report unplugged but the device as a whole stays on-line. If it were something like the DDF upgrade you mentioned, you should see some sensors off-line and others on-line. You would also see duplicates of the off-line sensors (or most of them).

Are all devices reporting sensor issues? If only some, are they all similar models or device types?

The issue you're speaking of with DDF updates on upgrade is also some time ago. I'm not aware of recent issues of this type except possibly with manual updates of 3rd party DDFs.

There is a possibility that there's an issue with the DDF(s) that are used to monitor the device, you could always look to update them or possibly upgrade DCE itself. If you've been running the server for 500+ days as noted in the k-base you linked, you're likely not on the most recent version.

 

Thanks,

Steve

(CID:148342532)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:46 PM . Last Modified: ‎2024-04-03 12:42 AM

In response to DCIM_Support
0 Likes
0
1842
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:46 PM . Last Modified: ‎2024-04-03 12:42 AM

Thanks Steve.

I'm seeing it only with our Eaton PDUs. (we're using modbus with these)
The various power sensors are reporting as expected but display names and other identifying information are showing as unplugged.
Strangely this behavior is inconsistent across PDUs; i.e. on one PDU a sensor reports a value as expected and on another it shows as unplugged.
The devices themselves are reporting any sensor issues.

I plan to upgrade to the latest version soon, but was hoping to resolve these issue before hand.

(CID:148344003)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:46 PM . Last Modified: ‎2024-04-03 12:42 AM

In response to DCIM_Support
0 Likes
0
1842
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:46 PM . Last Modified: ‎2024-04-03 12:42 AM

Hi John,

For a test, maybe try rebooting one of the effected network cards. Maybe re-run a discovery on the device (not delete it unless you don't care about old data) just re-run the discovery ads I have seen that correct some comm issues in the past. 

If it's numerous devices on the same gateway, perhaps rebooting the gateway might help. 

You might even want to reboot the DCE again. 

Sorry I don't have a specific fix for this but it'll take some troubleshooting.

 

Steve

(CID:148343999)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:46 PM . Last Modified: ‎2024-04-03 12:42 AM

In response to DCIM_Support
0 Likes
0
1842
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:46 PM . Last Modified: ‎2024-04-03 12:42 AM

Rebooting the NIC cards on the devices seems to work. Thanks for the advice.

(CID:148344006)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:46 PM . Last Modified: ‎2023-10-22 03:54 AM

0 Likes
0
1842
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:46 PM . Last Modified: ‎2023-10-22 03:54 AM

superhero.pngsuperhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore