Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Sensor Genome

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • 🔒 Closed
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:32 PM . Last Modified: ‎2024-04-03 02:37 AM

0 Likes
6
1637
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:32 PM . Last Modified: ‎2024-04-03 02:37 AM

Sensor Genome

We are using an Enviromux device as a back up for temperature monitoring in some of our smaller computer rooms. I want to be able to place the temperature sensors on a rack in DCO but am having issues creating a device that can be mounted on the rack, not in a rack. 

I have tried modifying a rack 0RU PDU and mounting the sensor on the side of a rack but the modified PDU still shows as 1400 long. 

There are "Device Sensors" attached to the racks that are associated with InRow Coolers and PDUs but they are not in the Genoms. 

There are also APC Temperature and Humidity sensors in the Genomos but all of them are 1RU and changing the Genome to 0RU and Left or Righ rear mounted makes no change. 

Any help would be appreciated 

(CID:143760555)

Labels
  • Labels:
  • Data Center Operation
  • Genome
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:32 PM . Last Modified: ‎2024-04-03 02:37 AM

0 Likes
2
1637
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:32 PM . Last Modified: ‎2024-04-03 02:37 AM

Hi Andrew

Not sure how to account for the physical asset in DCO,.  Perhaps you could allow it to be mounted on the top of the rack, at least that way it's in the "asset DB".  The temp sensor reading on the other hand can be placed on a rack in the DCO layout exactly where the probe is physically located on the rack. 

1. Is it being monitored by DCE? 

2. DCE integrated with DCO as an external system? 

3. the probe visible in Device Association? 

4. The temp sensor and it's value visible underneath the device? 

If all those things OK, drag and drop the sensor to the rack location.   If 1&2 are good but #4 isn't, that's usually a mod required to the DDF for DCE to expose the temp sensor to DCO in a very specific manner for DCO to "see it".

Hope all that helps

Cheers

Ed

 

(CID:143760561)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:32 PM . Last Modified: ‎2024-04-03 02:37 AM

In response to DCIM_Support
0 Likes
0
1637
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:32 PM . Last Modified: ‎2024-04-03 02:37 AM

Hi Ed

It is being monitored by DCE and the appliance is associated as an external system. The issue is that the sensors are mounted remotely and the only way that I can find of mounting them is to place them in the rack, in an RU.  I have configured the Gnome AP9335T to be able to be mounted on the Top, left or Right Rear. I have set the Width, Height and Depth to 100mm with hight at 0RU. I can then mount it in a rack but it's not visible. If I set the hight to 1RU then it will only mount in a rack unit, not on top or anywhere else. 

Is there a way to mount a device on the top of a rack or even on a wall?

(CID:143760651)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:32 PM . Last Modified: ‎2024-04-03 02:37 AM

In response to DCIM_Support
0 Likes
0
1637
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:32 PM . Last Modified: ‎2024-04-03 02:37 AM

Makes sense.  You have to set the mount options for the device to include "top" (of rack).  Not sure if you can do this for devices already in the model or you have to do it for the Genomes entry then place a new device. 

I believe you can also places sensors on the wall if you require.

Cheers

Ed

(CID:143760795)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:32 PM . Last Modified: ‎2024-04-03 02:37 AM

0 Likes
1
1637
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:32 PM . Last Modified: ‎2024-04-03 02:37 AM

If you are using DCO 8.3, there is also the possibility of using the new vertical u position feature in racks where you can create vertical U slots to the left or right rack sides and place a device there ... in this case you'd avoid consuming a rack U slot which counts against capacity reports.

Info regarding vertical U positions can be found here: https://sxwhelpcenter.ecostruxureit.com/display/UADCO8x/Adding+rack-mountable+equipment+to+the+room+...

Regards

GregS

(CID:144311112)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:32 PM . Last Modified: ‎2024-04-03 02:37 AM

In response to DCIM_Support
0 Likes
0
1637
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:32 PM . Last Modified: ‎2024-04-03 02:37 AM

Thanks Greg, this solves the issue completely 😀

 

Thanks 

(CID:144311114)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:32 PM . Last Modified: ‎2023-10-22 03:53 AM

0 Likes
0
1637
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:32 PM . Last Modified: ‎2023-10-22 03:53 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore