Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Same PDU Different Identification from DCE

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Same PDU Different Identification from DCE
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 01:03 AM . Last Modified: ‎2024-04-02 11:21 PM

0 Likes
8
2171
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 01:03 AM . Last Modified: ‎2024-04-02 11:21 PM

Same PDU Different Identification from DCE

Hello all,

I have 4 identical pdu's, that they worked fine with DCE.

I had to erase the XML file for a reason and when I reupload the xml file for these pdus the DCE identified three of them.

For the last one only the online sensor has been found and nothing else. What might happen?

Thank you

 

 

(CID:153944476)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 01:03 AM . Last Modified: ‎2024-04-02 11:21 PM

0 Likes
0
2171
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 01:03 AM . Last Modified: ‎2024-04-02 11:21 PM

Dear Grigorios Kousidis,

Please tell us the firmware version and model/part number of your rPDU.

Also, what do you mean by an XML file? If you mean a DDF-file, then what is its name and version?

Show a couple of screenshots from DCE and then they will help you faster and better 😀.

With respect.

(CID:153944491)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 01:03 AM . Last Modified: ‎2024-04-02 11:21 PM

0 Likes
0
2171
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 01:03 AM . Last Modified: ‎2024-04-02 11:21 PM

This is happen for 2 different type of pdus (borh Oracle) The first group is about 4 RMII_PDU24KVA-3_HV and the other one is about 6 RMII_PDU15KVA-3_HV

The first one is RMII_PDU24KVA-3_HV

Firmware version:V2.07 - 08.11.2016

Product Identifier:Exadata X6-2

 

The second one is RMII_PDU15KVA-3_HV

Firmware version:V2.04 - 27.05.2015

Product Identifier:ZDLRA X6

 

Sorry about the XML, I meant DDF

The xml file that I uploaded as DDF is "oracle_rmii_pdu.xml" and I downloaded from here.

As you can see in the attached file difference between the correct and the false identifications.

 

And the other type is the following

 

(CID:153944543)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 01:03 AM . Last Modified: ‎2024-04-02 11:21 PM

0 Likes
4
2171
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 01:03 AM . Last Modified: ‎2024-04-02 11:21 PM

Dear Grigorios Kousidis,

Since you are using two different models Oracle rPDU's, you need to download two separate DDF-files from the DDF resource, as in my screenshot:

Then import both DDF-files (simply import zip-file) and rediscover your Oracle rPDUs.

I hope this is what you need.

With respect.

(CID:153944567)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 01:03 AM . Last Modified: ‎2024-04-02 11:21 PM

In response to DCIM_Support
0 Likes
0
2171
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 01:03 AM . Last Modified: ‎2024-04-02 11:21 PM

I imported both DDF files and I still have the same issues.

In the same rack with the same pdu model- one of two cannot be recognized by DCE  the correct model / values/ sensors / serial number etc  as I send you before.

Will be helpful if I send you the SNMP Device walk for the correct and false pdus?

(CID:153944665)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 01:04 AM . Last Modified: ‎2024-04-02 11:21 PM

In response to DCIM_Support
0 Likes
0
2171
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 01:04 AM . Last Modified: ‎2024-04-02 11:21 PM

Dear Grigorios Kousidis,

In this case, please show a screenshot from the DCE-client with the names and versions of all SNMP DDF-files.

Please see your e-mail: I sent you my e-mail so that you send snmpwalk files as mentioned above.

With respect.

(CID:153944655)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 01:04 AM . Last Modified: ‎2024-04-02 11:21 PM

In response to DCIM_Support
0 Likes
0
2171
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 01:04 AM . Last Modified: ‎2024-04-02 11:21 PM

 

I'm sending you at the email you send me the snmpwalks

(CID:153944661)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 01:04 AM . Last Modified: ‎2024-04-02 11:21 PM

In response to DCIM_Support
0 Likes
0
2171
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 01:04 AM . Last Modified: ‎2024-04-02 11:21 PM

Ok, I see your e-mail and I will write you soon.

(CID:153944698)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 01:04 AM . Last Modified: ‎2023-10-22 03:51 AM

0 Likes
0
2171
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 01:04 AM . Last Modified: ‎2023-10-22 03:51 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore