Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Restoring DCE Server (AP9470) using Bootable Disk

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Re: Restoring DCE Server (AP9470) using Bootable Disk
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
160
Jef
Jef Leader
114
gsterling
gsterling Mentor
79
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
Tafadzwa
Tafadzwa
Contributor

Posted: ‎2023-10-11 05:15 AM

0 Likes
7
3067
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-10-11 05:15 AM

Restoring DCE Server (AP9470) using Bootable Disk

Hi all,

 

I am trying to Restore a Physical DCE Server (AP9470) that is running on ISX v7.0.0 using a Bootable disk created using a Restore ISO v7.81 however when the Server turns on it is throwing an Error - "Could not find kernel image: linux"

 

I have created the Bootable disk using a Windows machine on a 32GB USB Drive.

 

Kindly assist with pointers on how to resolve this?

 

Thank you in advance!

 

@gsterling 

@Gabi 

@Shaun 

Connecting Devices!
  • Tags:
  • Data Center Expert
  • dce
  • DCIM
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
dpierce4776
dpierce4776
Troubleshooter

Posted: ‎2023-10-11 08:50 PM

1 Like
0
3047
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-10-11 08:50 PM

@Tafadzwa You can not restore a DCE server to a different version than the one the backup was created for. So if you back up is from a 7.0.0 box you have to use a Restore ISO v7.0.0. Then restore your backup, and then upgrade to 7.8.1.

If you are looking to wipe the server and do a fresh install starting at 7.8.1 then the USB is fine, but really I would go ahead and get the newest version. I think they are on 8.0.0 or higher now. One thing I have found though is that while the instructions say to put the USB into a USB slot. Only one really works for this. When I had to do this I believe it was the top one on the back, was the only one that the BIOS would see and use.


Also make sure that you use the correct version of APC's key maker software that matches the ISO version that you are making the key for. This can usually be downloaded on the same page that you get the ISO from. Allow the Key maker program to format the USB stick/drive, and create the boot able Key for DCE. Then place the USB stick into one of the rear USB slots and reboot/power on the server. If you do not see the USB drive in the boot options then move it to the other USB slot and reboot the server again.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

dpierce4776
dpierce4776
Troubleshooter

Posted: ‎2023-10-19 03:27 PM

In response to Tafadzwa
0 Likes
0
2998
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-10-19 03:27 PM

@Tafadzwa You should really look for a smaller USB drive. I currently use a 4GB one and works great. what may be happening is that the server is trying to use the partition that has nothing on it to boot from

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Gabi
Gabi
Mentor

Posted: ‎2023-10-11 07:15 AM

0 Likes
2
3044
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-10-11 07:15 AM

hello,

 

first of all: did you use mkDCExpertRestoreUsbKey from Schneider to write iso on usb drive?

 

second: is recommended usb drive max 4gb (you can create a smaller partition on that usb drive)

 

optional you can try to boot that usb on any computer(of course do not start install because will erase internal drive) 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

dpierce4776
dpierce4776
Troubleshooter

Posted: ‎2023-10-11 08:50 PM

1 Like
0
3047
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-10-11 08:50 PM

@Tafadzwa You can not restore a DCE server to a different version than the one the backup was created for. So if you back up is from a 7.0.0 box you have to use a Restore ISO v7.0.0. Then restore your backup, and then upgrade to 7.8.1.

If you are looking to wipe the server and do a fresh install starting at 7.8.1 then the USB is fine, but really I would go ahead and get the newest version. I think they are on 8.0.0 or higher now. One thing I have found though is that while the instructions say to put the USB into a USB slot. Only one really works for this. When I had to do this I believe it was the top one on the back, was the only one that the BIOS would see and use.


Also make sure that you use the correct version of APC's key maker software that matches the ISO version that you are making the key for. This can usually be downloaded on the same page that you get the ISO from. Allow the Key maker program to format the USB stick/drive, and create the boot able Key for DCE. Then place the USB stick into one of the rear USB slots and reboot/power on the server. If you do not see the USB drive in the boot options then move it to the other USB slot and reboot the server again.

Reply

Link copied. Please paste this link to share this article on your social media post.

Tafadzwa
Tafadzwa
Contributor

Posted: ‎2023-10-12 11:52 AM

In response to Gabi
0 Likes
1
3029
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-10-12 11:52 AM

hi @Gabi 

 

I used the mkDCExpertRestoreUsbKey from Schneider. I created a smaller partion on the USB and I made it 4GB.

 

The Restore started running however it got stuck on "anaconda installer init version 13.21.263 using a serial console"

 

Any idea how to move from this?

 

Thank you.

Connecting Devices!
Reply

Link copied. Please paste this link to share this article on your social media post.

dpierce4776
dpierce4776
Troubleshooter

Posted: ‎2023-10-19 03:27 PM

In response to Tafadzwa
0 Likes
0
2998
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-10-19 03:27 PM

@Tafadzwa You should really look for a smaller USB drive. I currently use a 4GB one and works great. what may be happening is that the server is trying to use the partition that has nothing on it to boot from

Reply

Link copied. Please paste this link to share this article on your social media post.

TZT
TZT
Explorer

Posted: ‎2024-05-06 04:57 AM

0 Likes
2
2676
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-06 04:57 AM

Hola,

Yo tengo el mismo problema el servidor se queda en  "anaconda installer init version 13.21.263 using a serial console" y estoy usando un USB de 4GB

Reply

Link copied. Please paste this link to share this article on your social media post.

Tafadzwa
Tafadzwa
Contributor

Posted: ‎2024-05-07 04:35 AM

In response to TZT
0 Likes
1
2670
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-07 04:35 AM

Hi @TZT ,

 

Sorry, can you type in English so that I can assist you?

Connecting Devices!
Reply

Link copied. Please paste this link to share this article on your social media post.

TZT
TZT
Explorer

Posted: ‎2024-05-07 04:40 AM

In response to Tafadzwa
0 Likes
0
2660
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-07 04:40 AM

hi @Tafadzwa 

 

I used the mkDCExpertRestoreUsbKey from Schneider on 4GB USB .

 

The Restore started running however it got stuck on "anaconda installer init version 13.21.263 using a serial console"

 

Any idea how to move from this?

 

Thank you.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore