Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Real Time Monitoring of DCE

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Real Time Monitoring of DCE
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 04:38 PM . Last Modified: ‎2024-04-03 04:26 AM

0 Likes
3
1647
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:38 PM . Last Modified: ‎2024-04-03 04:26 AM

Real Time Monitoring of DCE

Hi Team,

We have a DCE in our office and its currently monitoring our UPS. What we notice is, some alarm are not being picked-up by the UPS. Like the fluctuation that cause the UPS to go on battery mode for several seconds, like 5-10 seconds. Also, during our genset operation, the transfer from normal-to-UPS power and vice versa, that cause the UPS to battery mode for about 20 seconds, is not picked up by DCE. No alarm has been registered on the DCE dashboard.

My question is, how real time is our DCE? Is it true that there are alarms that DCE can't detect because of time? Thank you.

(CID:138811205)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 04:38 PM . Last Modified: ‎2024-04-03 04:26 AM

0 Likes
1
1647
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:38 PM . Last Modified: ‎2024-04-03 04:26 AM

Roxan Grace,

DCE works by polling the devices.  The default polling interval is 5 minutes, but can be defined to be different within the Device Menu > SNMP Device Community Settings > Device Scan Settings.

APC (NMC) devices have the ability to utilize priority scanning.  Priority scanning takes place when an APC device has an active alarm.  An SNMP trap will be sent to the DCE server that will move the device scan towards the top of the queue.  DCE will then reach out to the device (SNMP) within a short period of time to check the device for what alarm may be active.  ModbusTCP devices do not have priority scanning as they work strictly on the polling interval and do not have a function similar to an SNMPtrap.

Additional information on priority scanning: 

https://www.apc.com/us/en/faqs/FA271584/

DCE does not take the trap and pull the error from it to add to the DCE alarm history.  It utilizes the SNMP scan from the priority scanning.  If an alarm is active when the priority scanning takes place it will then show the alarm within DCE.

It depends on the load on your server (number of devices, polling intervals, amount of sensors, surveillance, etc.) on how fast priority scanning takes place.  Usually it will take place within 30 seconds of an alarm going active on the device.

 

Here is an example of how this would work with your short time-frame alarms:

UPS on battery.

UPS NMC sends SNMPtrap to DCE (via priority scanning)

DCE recieves priority scanning & queues an SNMP scan.

12:00:20 - UPS no longer on battery.

DCE scans the device, but no alarm is active.

 

If the alarm stays active long enough, it would occur more like this:

UPS on battery.

UPS NMC sends SNMPtrap to DCE (via priority scanning)

DCE receives priority scanning & queues an SNMP scan.

DCE scans the device and sees the active alarm.

UPS no longer on battery.

 

Kind Regards,

Cory

(CID:138811215)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 04:38 PM . Last Modified: ‎2024-04-03 04:26 AM

0 Likes
1
1648
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:38 PM . Last Modified: ‎2024-04-03 04:26 AM

Roxan Grace,

DCE works by polling the devices.  The default polling interval is 5 minutes, but can be defined to be different within the Device Menu > SNMP Device Community Settings > Device Scan Settings.

APC (NMC) devices have the ability to utilize priority scanning.  Priority scanning takes place when an APC device has an active alarm.  An SNMP trap will be sent to the DCE server that will move the device scan towards the top of the queue.  DCE will then reach out to the device (SNMP) within a short period of time to check the device for what alarm may be active.  ModbusTCP devices do not have priority scanning as they work strictly on the polling interval and do not have a function similar to an SNMPtrap.

Additional information on priority scanning: 

https://www.apc.com/us/en/faqs/FA271584/

DCE does not take the trap and pull the error from it to add to the DCE alarm history.  It utilizes the SNMP scan from the priority scanning.  If an alarm is active when the priority scanning takes place it will then show the alarm within DCE.

It depends on the load on your server (number of devices, polling intervals, amount of sensors, surveillance, etc.) on how fast priority scanning takes place.  Usually it will take place within 30 seconds of an alarm going active on the device.

 

Here is an example of how this would work with your short time-frame alarms:

UPS on battery.

UPS NMC sends SNMPtrap to DCE (via priority scanning)

DCE recieves priority scanning & queues an SNMP scan.

12:00:20 - UPS no longer on battery.

DCE scans the device, but no alarm is active.

 

If the alarm stays active long enough, it would occur more like this:

UPS on battery.

UPS NMC sends SNMPtrap to DCE (via priority scanning)

DCE receives priority scanning & queues an SNMP scan.

DCE scans the device and sees the active alarm.

UPS no longer on battery.

 

Kind Regards,

Cory

(CID:138811215)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 04:38 PM . Last Modified: ‎2024-04-03 04:26 AM

In response to DCIM_Support
0 Likes
0
1647
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:38 PM . Last Modified: ‎2024-04-03 04:26 AM

Hi Cory,

Thank you very much for clarifying this one. I do now understand how the DCE processes the alarm notification. I will now have to check the scanning interval set to each of our devices and will utilize the priority scanning.

Thank you and Best Regards,

Roxan

(CID:138811262)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 04:38 PM . Last Modified: ‎2023-10-22 03:44 AM

0 Likes
0
1647
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:38 PM . Last Modified: ‎2023-10-22 03:44 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore