Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Random Alerts and Errant Notifications

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Re: Random Alerts and Errant Notifications
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
KSBTech
KSBTech
Explorer

Posted: ‎2024-08-15 04:23 AM

0 Likes
6
1989
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-15 04:23 AM

Random Alerts and Errant Notifications

RE: DCE 8.1.1

We get random alerts that DCE lost communication with a device, even though I can launch to the device from within DCE and there are no alerts on the device itself. Requesting a device scan does not make the alert go away and neither does rebooting the NMC on the device. The only effective way to get rid of these is to reboot the DCE server. And, unfortunately, every time I reboot the server, I then get tons of notifications from it about FTP logins to my devices and successful config.ini downloads. These issues have not been unique to the current build; it's been buggy like this for some time. When will these nuisance bugs get squashed?

Labels
  • Labels:
  • Data Center Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Cory_McDonald
Cory_McDonald Champion
Champion

Posted: ‎2024-09-11 05:57 AM

In response to KSBTech
0 Likes
0
1859
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-11 05:57 AM

Hello @KSBTech,

 

I was able to get some more information on this.  Upon a reboot DCE is getting config.ini files for each unique device configuration type.  Once DCE pulls a config.ini file that also applies to some other devices, those other devices will not have their config.ini files pulled.  So although this may appear to randomly select devices (likely based on next to be polled for each configuration type), it is expected behavior.

 

Kind Regards,

Cory

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Cory_McDonald
Cory_McDonald Champion
Champion

Posted: ‎2024-08-16 12:42 PM

0 Likes
4
1979
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-16 12:42 PM

Hello @KSBTech,

 

I'm going to separate this into two different issues, the first being that you are getting notifications based on the notifications that you are receiving after reboot about file transfers.  These must be configured on the NMC itself to send notifications when these actions occur.  You can modify these to not send an email if you choose by logging into the NMC interface and going to: Configuration > Notification > Event Actions > By Event.

 

The events that you are looking to configure would be found within the System Events heading.  This would allow you to disable those notifications from sending emails, but still log them in the event log.

 

For the second issue, if the communication lost events "stick" and never clear until a DCE reboot, I would recommend starting with an SNMPwalk from DCE's web interface.  If that walk does not work, there is usually either a device or network issue at that time.

 

the server may be having some performance issues or some other issue unique to device communication.  I would recommend reaching out to technical support with the following information:

  • DCE Serial Number
  • DCE MAC Address
  • Device Specific Information (for devices having the lost communication issues) such as Model & Firmware
  • Capture Log Files (likely will need to wait for technical support to send an upload link)
  • If the server is a VM, please provide VM resources (CPU, RAM, hard drives)

 

Kind Regards,

Cory

Reply

Link copied. Please paste this link to share this article on your social media post.

KSBTech
KSBTech
Explorer

Posted: ‎2024-08-19 04:52 AM

In response to Cory_McDonald
0 Likes
3
1935
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-19 04:52 AM

Thanks, Cory. So from your explanation, I gather that all of the events I'm seeing after a DCE reboot are legitimate actions that DCE is doing every time it is rebooted? It is logging into most/all devices and downloading config files on a random few? It's supposed to do that?

Reply

Link copied. Please paste this link to share this article on your social media post.

Cory_McDonald
Cory_McDonald Champion
Champion

Posted: ‎2024-08-29 07:17 AM . Last Modified: ‎2024-08-29 07:32 AM

In response to KSBTech
0 Likes
2
1933
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-29 07:17 AM . Last Modified: ‎2024-08-29 07:32 AM

Hello @KSBTech,

 

Data Center Expert will at times reach out to the end-devices to pull in a config.ini file.  I am not 100% sure of all of the triggers of this action, but a reboot could be one of them.

 

Update:  I ran a quick test and was able to see that upon a reboot there were some of my devices that had the config.ini file pulled.  This is likely a condition to ensure proper communication to certain device types and I would say that it is expected behavior.

 

Kind Regards,

Cory

Reply

Link copied. Please paste this link to share this article on your social media post.

KSBTech
KSBTech
Explorer

Posted: ‎2024-09-09 07:52 AM

In response to Cory_McDonald
0 Likes
1
1886
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-09 07:52 AM

Hi Cory,

 

I appreciate your response and the testing you did. I agree it's probably expected or known behavior, I'm just not sure I agree that it is correct behavior if it is decidedly random. If it pulled configs from all devices, I'd say it's by design, but random ones, not all of them, seems strange. Who knows? It's just a bit annoying as it creates a lot of unnecessary alert noise.

Reply

Link copied. Please paste this link to share this article on your social media post.

Cory_McDonald
Cory_McDonald Champion
Champion

Posted: ‎2024-09-11 05:57 AM

In response to KSBTech
0 Likes
0
1860
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-11 05:57 AM

Hello @KSBTech,

 

I was able to get some more information on this.  Upon a reboot DCE is getting config.ini files for each unique device configuration type.  Once DCE pulls a config.ini file that also applies to some other devices, those other devices will not have their config.ini files pulled.  So although this may appear to randomly select devices (likely based on next to be polled for each configuration type), it is expected behavior.

 

Kind Regards,

Cory

Reply

Link copied. Please paste this link to share this article on your social media post.

KSBTech
KSBTech
Explorer

Posted: ‎2024-09-11 05:58 AM

1 Like
0
1841
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-11 05:58 AM

Understood. Thanks again.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore