Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Question about DDF file transfers

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Question about DDF file transfers
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 04:37 PM . Last Modified: ‎2024-04-05 12:10 AM

0 Likes
3
1441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:37 PM . Last Modified: ‎2024-04-05 12:10 AM

Question about DDF file transfers

Not a problem exactly more a question of curiosity.

DDF's are uploaded to the server, but the knowledge base https://www.schneider-electric.us/en/faqs/FA177004/ states:-

"StruxureWare Data Center Expert uses device definition files (DDF) to understand what information to poll and how to format different information from discovered devices. During discovery of APC devices and after a firmware update of APC devices, the StruxureWare server will attempt to download DDF files from the device using FTP or SSH. If the server is unable to perform this transfer, you will see a message stating "Device status may be inaccurate due to attempt to transfer DDF failed"."

So do the DDF's reside on the device or the DCE server?

If they are on the device then why do we upload them to the DCE server?

Does that transfer actually go from the server to the device?

Is it just that on APC/Schneider devices the DDF's reside on the device(s)?

If the DDF's for APC devices do come from the devices themselves, what happens regarding the DDF version when devices with the same model number but different firmware versions are monitored by the same DCE server?

Thanks in advance.


 

 

(CID:130096190)

Labels
  • Labels:
  • Data Center Expert
  • DDF
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 04:37 PM . Last Modified: ‎2024-04-05 12:10 AM

0 Likes
1
1441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:37 PM . Last Modified: ‎2024-04-05 12:10 AM

Hi Garry,

 

There are often multiple DDFs in use at one time. The 2 main DDFs being used by APC devices are the "scanner" DDF and the "alerts" DDF. Some devices often use more than 1 scanner DDF as well as a UPS may have environmental functionality etc. 

The scanner DDF resides on the DCE server. It is used to tell DCE what data points to poll. These are what you see in reports and if you right click a device and choose to view device sensors. This DDF is updated when you update your DCE version or when you manually choose to update DDFs.

The alerts DDF is stored on the APC device and transferred to DCE when the device is discovered or it's firmware is updated.  These DDFs tell DCE what they should alert for on that specific device. If you go to the alarm configurations perspective in DCE, you'll see that APC devices have numerous pre-configured alerts in the device alarm configurations tab. These alarms come from that DDF that is transferred from the device itself. DCE then keeps track of which alert DDF to use for each device/firmware in the off chance that you update firmware (and subsequently the alert DDF) for some devices and not others.

There are a few third party devices that have pre-configured alarms here as well and they are built into the scanner DDFs. With APC devices however, newer firmware may have new alarm options and by putting the alarm DDF on that device/firmware, the firmware developers for device itself dictate what device alarms are written in to the DDF.


Steve

(CID:130096200)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 04:37 PM . Last Modified: ‎2024-04-05 12:10 AM

0 Likes
1
1442
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:37 PM . Last Modified: ‎2024-04-05 12:10 AM

Hi Garry,

 

There are often multiple DDFs in use at one time. The 2 main DDFs being used by APC devices are the "scanner" DDF and the "alerts" DDF. Some devices often use more than 1 scanner DDF as well as a UPS may have environmental functionality etc. 

The scanner DDF resides on the DCE server. It is used to tell DCE what data points to poll. These are what you see in reports and if you right click a device and choose to view device sensors. This DDF is updated when you update your DCE version or when you manually choose to update DDFs.

The alerts DDF is stored on the APC device and transferred to DCE when the device is discovered or it's firmware is updated.  These DDFs tell DCE what they should alert for on that specific device. If you go to the alarm configurations perspective in DCE, you'll see that APC devices have numerous pre-configured alerts in the device alarm configurations tab. These alarms come from that DDF that is transferred from the device itself. DCE then keeps track of which alert DDF to use for each device/firmware in the off chance that you update firmware (and subsequently the alert DDF) for some devices and not others.

There are a few third party devices that have pre-configured alarms here as well and they are built into the scanner DDFs. With APC devices however, newer firmware may have new alarm options and by putting the alarm DDF on that device/firmware, the firmware developers for device itself dictate what device alarms are written in to the DDF.


Steve

(CID:130096200)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 04:37 PM . Last Modified: ‎2024-04-05 12:10 AM

In response to DCIM_Support
0 Likes
0
1441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:37 PM . Last Modified: ‎2024-04-05 12:10 AM

Thanks for the quick answer.

It makes a bit more sense now.  A bit more complicated than it first seems

 

Thanks again

(CID:130096245)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 04:38 PM . Last Modified: ‎2023-10-22 03:40 AM

0 Likes
0
1441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:38 PM . Last Modified: ‎2023-10-22 03:40 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore