Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Powertag Power readings are not correctly shown in DCE

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Powertag Power readings are not correctly shown in DCE
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 08:58 PM . Last Modified: ‎2024-04-03 01:01 AM

0 Likes
3
1516
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 08:58 PM . Last Modified: ‎2024-04-03 01:01 AM

Powertag Power readings are not correctly shown in DCE

 

Hello community,

 

We are having trouble with reading power values via powertags in DCE . We added 4 acti 9 smartlink devices in DCE with 20 powertags connected wirelessly to each of them. 

When access directly to web server of acti 9 smartlinks we can read the power values as shown at the screenshot below ; 

 

 

But in DCE ; link status is online , data looks corrupted .

 

Devices are being added in modbus tcp device add section.For device type i can only choose " Acti9 Smartlink Modbus " to make it online.

I have downloaded and imported the two DDF files from DDF library portal which are related with Acti9 devices. Slave address of smartlinks looks impossible to change they are all 255 . İ couldnt at least. When i delete the other discovered smartlinks and tried out just one with same 255 slave address also couldnt have success in power readings. I think slave address section is not the subject in this situation.

We use powertag 1560 and 1570 models. Smartlink devices are upgraded to latest 2.2.7 firmware. Data Center Expert is not yet upgraded to R 7.6  .Its a phsiycal appliance running with delivery Release 7.4.1. 

I hope i could explain the problem. Any advice that you give me would be highly appreciated. 

Thanks in advance.

 

Best regards.

Ozgur.

(CID:147198240)

Labels
  • Labels:
  • Data Center Expert
  • DDF
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 08:58 PM . Last Modified: ‎2024-04-03 01:01 AM

0 Likes
1
1518
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 08:58 PM . Last Modified: ‎2024-04-03 01:01 AM

Hi Ozgur,

Because you are using Powertag sensors, I think you have an Acti9 Smartlink SI B or D.  In this case, you will want to use the "schneider_acti9_smartlinksid.xml" DDF which you can download from the DDF download page (it looks like you are using the DDF with the file named "schneider_acti9_smartlink.xml" - the names are so similar, this can be confusing).

In addition to using that DDF, you will want to enter the slave address of the Powertag sensor, not the Acti9 itself.  The Acti9 will assign the sensors the Modbus slave address automatically, so you will probably have to look in the Acti9 configuration to know which addresses go with which sensors.

From page 79 of the Smartlink SI D manual:  "Acti9 Smartlink SI D allocates dynamically, a slave number 150 through 169 for each of the 20 wireless communication devices (up to 20 wireless communication devices) that could be connected to the Acti9 Smartlink SI D."

 

Let us know if this resolves your issue.

Jake

(CID:147198453)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 08:58 PM . Last Modified: ‎2024-04-03 01:01 AM

0 Likes
1
1519
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 08:58 PM . Last Modified: ‎2024-04-03 01:01 AM

Hi Ozgur,

Because you are using Powertag sensors, I think you have an Acti9 Smartlink SI B or D.  In this case, you will want to use the "schneider_acti9_smartlinksid.xml" DDF which you can download from the DDF download page (it looks like you are using the DDF with the file named "schneider_acti9_smartlink.xml" - the names are so similar, this can be confusing).

In addition to using that DDF, you will want to enter the slave address of the Powertag sensor, not the Acti9 itself.  The Acti9 will assign the sensors the Modbus slave address automatically, so you will probably have to look in the Acti9 configuration to know which addresses go with which sensors.

From page 79 of the Smartlink SI D manual:  "Acti9 Smartlink SI D allocates dynamically, a slave number 150 through 169 for each of the 20 wireless communication devices (up to 20 wireless communication devices) that could be connected to the Acti9 Smartlink SI D."

 

Let us know if this resolves your issue.

Jake

(CID:147198453)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 08:58 PM . Last Modified: ‎2024-04-03 01:01 AM

In response to DCIM_Support
0 Likes
0
1518
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 08:58 PM . Last Modified: ‎2024-04-03 01:01 AM

Hi Jake,

Thank you very much for your help. Your information about adding powertags seperately with the same ip address of smartlink SI D,  but with unique slave address solved my issue. I tought that just adding smartlink will be enough for viewing powertags running behind it and i now see it was so wrong. Finally i will submit the project. It was urgent.

Thanks a lot again.

😀

Best regards.

Ozgur.

(CID:147198584)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 08:59 PM . Last Modified: ‎2023-10-22 03:37 AM

0 Likes
0
1518
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 08:59 PM . Last Modified: ‎2023-10-22 03:37 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore