Dear colleagues,
I have updated the Power Outlet name on EPDU116S Rack PDU however on DCE the default Outlet name is still showing under Device Sensors.
I need the same naming conversion on the R-PDU to show on DCE.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-03-12 05:15 AM
Hi @Mr._T ,
Assuming that value is available in the SNMP output, it would require an updated DDF in order to get those values into the DCE system or, even if they're listed when you right click to view device sensors and they're available from that view, the DDF would need to be changed to get the values to the place that you believe they should be.
I don't have an EZ PDU available so I suggest doing an SNMPwalk of the device (can be done from the web page of DCE) and contacting support with the pertinent info. They can send it to the DDF team.
Thanks,
Steve
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-03-12 05:15 AM
Hi @Mr._T ,
Assuming that value is available in the SNMP output, it would require an updated DDF in order to get those values into the DCE system or, even if they're listed when you right click to view device sensors and they're available from that view, the DDF would need to be changed to get the values to the place that you believe they should be.
I don't have an EZ PDU available so I suggest doing an SNMPwalk of the device (can be done from the web page of DCE) and contacting support with the pertinent info. They can send it to the DDF team.
Thanks,
Steve
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.