Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PDU firmware update progress hangs

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Re: PDU firmware update progress hangs
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
160
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 09:06 AM . Last Modified: ‎2024-04-08 03:39 AM

0 Likes
7
1657
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:06 AM . Last Modified: ‎2024-04-08 03:39 AM

PDU firmware update progress hangs

Hello,

I have updated the firmware on four of my PDUS but two have hung (for days) with the message Waiting for RPDU2G 6.4.4 to load....

The PDUS are both AP8653 models

I have rebooted the management server and the pdus.

If i launch directly to the pdu i see that its running 6.4.4.

How can i update the firmware update page to show these puds as being upgraded?

Thanks

Patrick

(CID:110008131)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 09:07 AM . Last Modified: ‎2024-04-08 03:39 AM

0 Likes
1
1657
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:07 AM . Last Modified: ‎2024-04-08 03:39 AM

Not an expert here but wanted to suggest some things:

Have you verified the SNMP settings, username/password DCE uses and also right click on the device and click  "Request Device Scan".

If the device is updated, I would like DCE should notice that in a few minutes but it sounds like DCE isn't getting a response back from the device.

Do you get alarms? trends?

Regards,

J

(CID:110008149)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 09:07 AM . Last Modified: ‎2024-04-08 03:39 AM

In response to DCIM_Support
0 Likes
0
1657
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:07 AM . Last Modified: ‎2024-04-08 03:39 AM

I dont have any alarms configured but if i setup a report it can retrieve the data which I thought used SNMP.

(CID:110008152)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 09:07 AM . Last Modified: ‎2024-04-08 03:39 AM

0 Likes
1
1657
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:07 AM . Last Modified: ‎2024-04-08 03:39 AM

Hi Patrick,

 

It looks like DCE is simply stuck looking to verify the version of firmware. What version of DCE are you using?

The first thing I would suggest is to reboot the server.

I'd also be curious to know if you went back to the firmware upgrade page (where you initiated the upgrade of the PDUs), does it show the correct firmware or is it prompting you to be able to upgrade the firmware again? 

Is it just these 2 PDUs? Do you have others that worked?

 

Thanks,

Steve

(CID:110008168)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 09:07 AM . Last Modified: ‎2024-04-08 03:39 AM

In response to DCIM_Support
0 Likes
0
1657
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:07 AM . Last Modified: ‎2024-04-08 03:39 AM

Hi Steve, I have already rebooted the server and the management interfaces of the PDUs. it shows the PDU as running app and os version 6.4.4, if I logon to the PDU it also says its running 6.4.4. The management server is running Client Build: 7.4.1.5 and Server Build: 7.4.1.5. there are two other PDUs in the same segment that updated fine. Regards Patrick

(CID:110008450)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 09:07 AM . Last Modified: ‎2024-04-08 03:38 AM

0 Likes
0
1657
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:07 AM . Last Modified: ‎2024-04-08 03:38 AM

I ended up deleting and recreating the two offending PDUs.

(CID:110008516)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 09:07 AM . Last Modified: ‎2024-04-08 03:38 AM

0 Likes
0
1657
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:07 AM . Last Modified: ‎2024-04-08 03:38 AM

Sorry to hear that. I knew that would resolve it but that causes the loss of historrical data and I would hope there would have been a less intrusive resolution. Thanks for the update Steve

(CID:110008519)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 09:07 AM . Last Modified: ‎2023-10-22 03:30 AM

0 Likes
0
1657
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:07 AM . Last Modified: ‎2023-10-22 03:30 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore