Ask our Experts
Didn't find what you are looking for? Ask our experts!
New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Search in
Please select a country to continue with beta search.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-01-03 06:51 AM
Are NetBotz Sensors, T, H & TH, monitor sensors capable to monitor Outdoor environment- eg, Outdoors of a Prefab.
Do they need to be placed in a IP rated shelters / cabinets / protected etc.
What is the environmental impact on the sensors- eg. from Rain, Snow, dust extreme heat & wind? Are there any IP ratings involved? Or Any specific IP rated NB sensors are orderable?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-01-03 07:45 AM
Hi @sesa241642 ,
NetBotz and it's associated sensors are designed for indoor use only. They are designed for use in an IT environment.
If you look at the following sensor for instance:
https://www.apc.com/shop/us/en/products/APC-Temperature-Humidity-Sensor/P-AP9335TH
You can see:
Operating Temperature
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.