Posted: 2020-07-05 12:29 PM . Last Modified: 2024-04-04 12:51 AM
Good day
Please assist.
I am struggling to enable the web server configuration ( under appliance window of configuration tab), the advance tab - it is blank.

Appliance details - Wallbotz 500
Any ideas ?
Thank you to all for assising!
Kind regards
(CID:134680935)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 12:29 PM . Last Modified: 2024-04-04 12:51 AM
Hi Juice,
I always recommend using a matching Advanced View software and NetBots "BotzWare" firmware. The highest level of BotzWare available for a WallBot 500 is 2.6.2. When using a version of Advanced View that does not match that, you will potentially see options in the software that are unavailable in the BotzWare.
This is one of those cases. Version 2 NetBotz appliances such as the 320, 420, and 500 do not support this feature. The entire web server configuration applet in Advanced View 2.6.2 looks like this:

There is no "advanced" option.
Thanks,
Steve
(CID:134681051)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 12:29 PM . Last Modified: 2023-10-22 03:24 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.