Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Netbotz 750 wireless sensor update via url or utility?

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • πŸ”’ Closed
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
160
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: β€Ž2020-07-05 10:38 PM . Last Modified: β€Ž2024-04-03 12:24 AM

0 Likes
5
2016
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-05 10:38 PM . Last Modified: β€Ž2024-04-03 12:24 AM

Netbotz 750 wireless sensor update via url or utility?

Does the netbotz 750 support the wireless sensor update url below or only via the netbotz web interface? 

http:///argusmenu


Also has a new wireless sensor update utility been released?  I've asked about it previously and seen other questions regarding it, but haven't seen an updated version?

(CID:149783145)

Labels
  • Labels:
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: β€Ž2020-07-05 10:38 PM . Last Modified: β€Ž2024-04-03 12:24 AM

0 Likes
3
2015
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-05 10:38 PM . Last Modified: β€Ž2024-04-03 12:24 AM

Hi Andrew,

 

Good day!

 

The link that you have given only applies to Netbotz v3 (450, 570). If the Netbotz 750's firmware is updated, the wireless sensor's firmware will be available from the appliance.

 

To update the firmware of the wireless device(s), go to the "Wireless" section/tab, and update the firmware on the wireless device if the "target" firmware version does not match the current firmware version.

 

The two-step process below describes the firmware update:

  1. Select Update then click yes. The target firmware is loaded to your wireless devices. This still requires implementation.
  2. When the update is successfully loaded, click the apply button to implement the update file.


Here in our lab, the Netbotz 750 wireless firmware update was quicker compared to the firmware update (Wireless) in Netbotz v3.

Regards,

 

Justine

(CID:149783253)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: β€Ž2020-07-05 10:38 PM . Last Modified: β€Ž2024-04-03 12:24 AM

0 Likes
3
2016
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-05 10:38 PM . Last Modified: β€Ž2024-04-03 12:24 AM

Hi Andrew,

 

Good day!

 

The link that you have given only applies to Netbotz v3 (450, 570). If the Netbotz 750's firmware is updated, the wireless sensor's firmware will be available from the appliance.

 

To update the firmware of the wireless device(s), go to the "Wireless" section/tab, and update the firmware on the wireless device if the "target" firmware version does not match the current firmware version.

 

The two-step process below describes the firmware update:

  1. Select Update then click yes. The target firmware is loaded to your wireless devices. This still requires implementation.
  2. When the update is successfully loaded, click the apply button to implement the update file.


Here in our lab, the Netbotz 750 wireless firmware update was quicker compared to the firmware update (Wireless) in Netbotz v3.

Regards,

 

Justine

(CID:149783253)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: β€Ž2020-07-05 10:38 PM . Last Modified: β€Ž2024-04-03 12:24 AM

In response to DCIM_Support
0 Likes
0
2015
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-05 10:38 PM . Last Modified: β€Ž2024-04-03 12:24 AM

Justine,

Thank you for confirming, I assumed as much about the v3 url, but wanted to confirm.  

 

Can someone comment on if/when a new update wireless firmware update utility will be released?  Although the minority, I know of customers that have a large netbot 250/wireless sensor deployment and without that utility, they are unable to update their wireless sensor firmware.

(CID:149783723)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: β€Ž2020-07-05 10:38 PM . Last Modified: β€Ž2024-04-03 12:24 AM

In response to DCIM_Support
0 Likes
0
2015
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-05 10:38 PM . Last Modified: β€Ž2024-04-03 12:24 AM

Hi Andrew,

 

Good day and I apologize for the late reply.

The Netbotz wireless firmware update utility can still be used to update the wireless coordinator/sensor. See the link below to download the latest available version.

Click here

 

As for the firmware update files, I recommend contacting technical support so they can share the updated files (for v1.1.1, v1.1.2, and v1.1.4) that you can use.

I hope this helps.

 

Regards,

 

Justine


(CID:149784588)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: β€Ž2020-07-05 10:38 PM . Last Modified: β€Ž2024-04-03 12:24 AM

In response to DCIM_Support
0 Likes
0
2015
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-05 10:38 PM . Last Modified: β€Ž2024-04-03 12:24 AM

Thank you, I'm a little surprised that APC didn't update the download on apc.com to include the new wireless firmware with the utility, but so be it.  If it comes up, I'll direct my customers to tech support to get them.

(CID:149784838)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: β€Ž2020-07-05 10:38 PM . Last Modified: β€Ž2023-10-22 03:21 AM

0 Likes
0
2015
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-05 10:38 PM . Last Modified: β€Ž2023-10-22 03:21 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore