Posted: 2024-07-17 02:04 PM
Can you provide a wiring example on how to wire a 4-20ma temperature transmitter utilizing the 24v DC output on the Netbotz 750 as the power source feeding the temperature transmitter and the 4-20ma input from the temperature sensor/ transmitter? I assume it would work like the drawings below.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-07-30 05:59 AM . Last Modified: 2024-07-30 06:23 AM
Hello @MattTripp,
This would depend on the specs of the sensor. If you have the specs/manual of the sensor, someone here may be able to provide assistance. 4-20mA sensor wiring could be 2 wire, 3-wire, or 4 wire. Usually the manual of the sensor will outline exactly how the electrical connections must be installed and any safety precautions or warnings with the installation/use of the sensor.
The voltage output can also only put out 75 mA of current, which often is not enough for the sensor depending on the 4-20mA sensor requirements.
Kind Regards,
Cory
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.