Netbotz 750 4-20ma input sensors wiring
Select a Country
  • Netbotz 750 4-20ma input sensors wiring
Cory_McDonald Champion
160
Jef Leader
114
gsterling Mentor
77
MattTripp
MattTripp Explorer
Explorer
Posted: ‎2024-07-17 02:04 PM
1586
Can you provide a wiring example on how to wire a 4-20ma temperature transmitter utilizing the 24v DC output on the Netbotz 750 as the power source feeding the temperature transmitter and the 4-20ma input from the temperature sensor/ transmitter? I assume it would work like the drawings below.
  • NetBotz
Champion
Posted: ‎2024-07-30 05:59 AM . Last Modified: ‎2024-07-30 06:23 AM
1505
Hello @MattTripp,
This would depend on the specs of the sensor.  If you have the specs/manual of the sensor, someone here may be able to provide assistance.  4-20mA sensor wiring could be 2 wire, 3-wire, or 4 wire.  Usually the manual of the sensor will outline exactly how the electrical connections must be installed and any safety precautions or warnings with the installation/use of the sensor.
The voltage output can also only put out 75 mA of current, which often is not enough for the sensor depending on the 4-20mA sensor requirements.
Kind Regards,
Cory
MattTripp
MattTripp Explorer
Explorer
Posted: ‎2024-07-30 03:06 PM
In response to Cory_McDonald
Thank you for your response Cory. I have uploaded the tech info and install info for a sensor that I am considering. It appears to be 2 wire application and draws 20ma max power. Therefore, I assume it could be wired as previously shown, would you agree?