Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Netbotz 450 not loading all boot processes

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Netbotz 450 not loading all boot processes
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 12:16 AM . Last Modified: ‎2024-04-04 12:57 AM

0 Likes
3
1552
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 12:16 AM . Last Modified: ‎2024-04-04 12:57 AM

Netbotz 450 not loading all boot processes

Hello All, I have recently encountered a puzzling issue with a Netbotz 450. Connecting to it serially via terminal. The appliance hangs while booting up, see below:

The appliance hangs at Net: FCC1 ETHERNET

Note: appliance is operating with the latest firmware, date of manufacture: 2018/03/09. 

Nothing loads after that. What might be causing this issue?

 

U-Boot 1.1.4 (Oct 31 2017 - 14:32:43)

MPC8248 Reset Status: External Soft, External Hard

MPC8248 Clock Configuration
- Bus-to-Core Mult 3x, VCO Div 4, 60x Bus Freq 16-50 , Core Freq 50-150
- dfbrg 0, corecnf 0x10, busdf 3, cpmdf 1, plldf 0, pllmf 3
- vco_out 400000000, scc_clk 100000000, brg_clk 100000000
- cpu_clk 300000000, cpm_clk 200000000, bus_clk 100000000
- pci_clk 33333333

CPU: MPC8248 (HiP7 Rev 14, Mask 1.0 1K50M) at 300 MHz
Watchdog enabled
I2C: ready
DRAM: 128 MB
FLASH: 64 MB
PCI Scan: Found Bus 0, Device 22, Function 0
PCI Scan: Found Bus 0, Device 22, Function 1
PCI Scan: Found Bus 0, Device 22, Function 2
In: serial
Out: serial
Err: serial
Net: FCC1 ETHERNET

(CID:134038009)

Labels
  • Labels:
  • NetBotz
  • Tags:
  • bug
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 12:17 AM . Last Modified: ‎2024-04-04 12:57 AM

0 Likes
1
1552
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 12:17 AM . Last Modified: ‎2024-04-04 12:57 AM

Hi Thabos,

 

I've seen a few instances where the reset button has been stuck "in" and it can cause the boot to hang or the system to constantly reboot. My first suggestion is to get a paper clip and push in on the reset button and move it around a little to see if that resolves the issue. 

Other than that, it might be a firmware issue. I'm not sure where these lines are in the boot process but if it gets past the u-boot load (where it says press any key within 10, 9, 8....) then I would suggest reflashing the firmware using the tftp flash procedure here:

 

Thanks,

Steve.

(CID:134038137)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 12:17 AM . Last Modified: ‎2024-04-04 12:57 AM

0 Likes
1
1553
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 12:17 AM . Last Modified: ‎2024-04-04 12:57 AM

Hi Thabos,

 

I've seen a few instances where the reset button has been stuck "in" and it can cause the boot to hang or the system to constantly reboot. My first suggestion is to get a paper clip and push in on the reset button and move it around a little to see if that resolves the issue. 

Other than that, it might be a firmware issue. I'm not sure where these lines are in the boot process but if it gets past the u-boot load (where it says press any key within 10, 9, 8....) then I would suggest reflashing the firmware using the tftp flash procedure here:

 

Thanks,

Steve.

(CID:134038137)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 12:17 AM . Last Modified: ‎2024-04-04 12:57 AM

In response to DCIM_Support
0 Likes
0
1552
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 12:17 AM . Last Modified: ‎2024-04-04 12:57 AM

Hi Steve

Thanks for the response, I'll check if the reset button is stuck. i have a feeling that might be the cause. 😀

as for where it says press any key within 10, 9, 8....). the boot procedure doesn't reach that point. 

 

(CID:134038431)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 12:17 AM . Last Modified: ‎2023-10-22 03:19 AM

0 Likes
0
1552
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 12:17 AM . Last Modified: ‎2023-10-22 03:19 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore