Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Netbotz 250 not discovered by DCE

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Netbotz 250 not discovered by DCE
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
160
Jef
Jef Leader
114
gsterling
gsterling Mentor
79
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 01:40 PM . Last Modified: ‎2024-04-05 02:52 AM

0 Likes
6
1269
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 01:40 PM . Last Modified: ‎2024-04-05 02:52 AM

Netbotz 250 not discovered by DCE

Hi Team,

in DCE 7.5 we are trying to discover a Netbotz 250, and we only find it with a SNMP discover, not with Netbotz discover.

We have updated the Netbotz's firmware to the last one, From a PC in the same network we can access to the Netbotz through a web browser, so we think there are not networks problems.

Also we have the alarm "Device status may be inaccurate because an attempt to transfer a device definition file (DDF) failed", and FTP is configured properly with port 21 and user/pass.

Regards.

 

(CID:128750596)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 01:40 PM . Last Modified: ‎2024-04-05 02:52 AM

0 Likes
4
1269
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 01:40 PM . Last Modified: ‎2024-04-05 02:52 AM

Hi Javier,

 

The NetBotz 250 is based on the technology of the network management card as is installed in a UPS etc and is not like the 3xx, 4xx, 5xx NetBotz devices monitored using http/https. K-base FA225604 also points this out.


Thanks,

Steve

(CID:128750606)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 01:40 PM . Last Modified: ‎2024-04-05 02:52 AM

In response to DCIM_Support
0 Likes
0
1269
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 01:40 PM . Last Modified: ‎2024-04-05 02:52 AM

Thanks Steven,

And the alarm about DDF transfering failure? We have the same alarm in a Smart-UPS RT 1500 RM XL.

Regards

(CID:128750617)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 01:40 PM . Last Modified: ‎2024-04-05 02:52 AM

In response to DCIM_Support
0 Likes
0
1269
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 01:40 PM . Last Modified: ‎2024-04-05 02:52 AM

Hi Javier,

Sorry I overlooked that part of the question. This too is in k-base. Take a look at k-base FA177004 as this outlines that issue.

 

Steve

(CID:128750622)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 01:40 PM . Last Modified: ‎2024-04-05 02:52 AM

In response to DCIM_Support
0 Likes
0
1269
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 01:40 PM . Last Modified: ‎2024-04-05 02:52 AM

Hi Steven Marchetti,

we have upgraded the firmware of all our Netbotz 200 and 250, and we have still the DDF Transfer Failure Alarm on these devices in DCE. 

Is there anyway to fix these alarms without aknowledgment them?

Best regards

(CID:128754385)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 01:40 PM . Last Modified: ‎2024-04-05 02:52 AM

In response to DCIM_Support
0 Likes
0
1269
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 01:40 PM . Last Modified: ‎2024-04-05 02:52 AM

Hi Javier,

When you upgraded the firmware on the devices, did you do so through DCE or outside of it? As per the k-base, this issue is due to the DCE server being unable to download the DDF using FTP (or scp) from the device. This should use the same protocol so if one works, the other should as well. That k-base should resolve the issue. If you'vegot the right user name and password and it can reach the 250, maybe try deleting and rediscovering one again.

Steve

(CID:128754395)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 01:40 PM . Last Modified: ‎2023-10-22 03:17 AM

0 Likes
0
1269
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 01:40 PM . Last Modified: ‎2023-10-22 03:17 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore