Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Netbotz 200 lost all sensors and stuck.

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Re: Netbotz 200 lost all sensors and stuck.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
160
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:16 PM . Last Modified: ‎2024-04-03 02:43 AM

0 Likes
8
2503
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:16 PM . Last Modified: ‎2024-04-03 02:43 AM

Netbotz 200 lost all sensors and stuck.

It worked correctly for a long time in connection with one extension module.

A couple weeks ago it start loosing connection to ext. module and throw alarms.

I tried to change cables, reboot modules, reset to factory settings. Nothing helped after reboot it detect module but lost connection in 20 minutes or less.

Now I tried to update firmware to lastest available (3.7.5). Process was finished without errors but now unit stuck at state where it throw events to log around every two minutes
"MM: Firmware downloading started for 'Unknown' at 'Unknown'."

If read event.txt through FTP there is also such lines:

 

MM: Firmware downloading started for 'Unknown' at 'Unknown'.    0x2E29

MM: Firmware downloading started for 'Unknown' at 'Unknown'.    0x2E29

MM: Firmware downloading started for 'Unknown' at 'Unknown'.    0x2E29

System: Network service started. System IP is 192.168.222.12 from manually configured settings.    0x0007

System: Warmstart.    0x0002

MM: Firmware downloading started for 'Unknown' at 'Unknown'.    0x2E29

MM: Firmware downloading started for 'Unknown' at 'Unknown'.    0x2E29

 

And all module resources(sensors, relay) reporting 'Err' state.

Is there a way to revive unit?

(CID:143757697)

Labels
  • Labels:
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:16 PM . Last Modified: ‎2024-04-03 02:43 AM

0 Likes
1
2501
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:16 PM . Last Modified: ‎2024-04-03 02:43 AM

Hi, 

You might want to try to connect back the extension module one by one. For example, initially, you have 3 extension module, and one of the extension modules lost communication due to cable issue or other reason. What you can do:

  1. Disconnect extension module to Netbotz, place the terminator to the Netbotz A-Link. Check if Netbotz itself is in normal condition. If yes, proceed to 2.
  2. Connect Netbotz to the first extension module, with the end terminator at the A-Link port of the extension module.
  3. Check if the Netbotz able to detect the module. 
  4. Continue to the next module, place the end terminator to the next module.
  5. Continue to the last one. 

Hope this helps. 

 

BR

TJ. 

 

(CID:143757783)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:16 PM . Last Modified: ‎2024-04-03 02:43 AM

In response to DCIM_Support
0 Likes
0
2501
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:16 PM . Last Modified: ‎2024-04-03 02:43 AM

I can not pass 1 because it stuck at "MM: Firmware downloading started for 'Unknown' at 'Unknown'.    0x2E29".

 

(CID:143757934)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:16 PM . Last Modified: ‎2024-04-03 02:42 AM

0 Likes
4
2501
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:16 PM . Last Modified: ‎2024-04-03 02:42 AM

Hi Serg,

 

Good day!

You might want to reset the Netbotz 200 to its factory default state, ruling out any possible hardware issues.

 

To reset the Netbotz 200, go to Administration-> General-> Reset/Reboot. Once you are on that page, select Reset All, then put a check under exclude TCP/IP (to retain the set IP address).

If this does not clear the error, you might want to apply the latest firmware version v3.9.0 that can be downloaded from the article from the link below:

https://www.schneider-electric.us/en/faqs/FA279764/

 

I hope this helps.

 

Regards,

Justine

(CID:143759189)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:16 PM . Last Modified: ‎2024-04-03 02:42 AM

In response to DCIM_Support
0 Likes
0
2501
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:16 PM . Last Modified: ‎2024-04-03 02:42 AM

Reset was done multiple times already.

Actually it stuck at MM: Firmware downloading started for 'Unknown' at 'Unknown'.    0x2E29

after upgrade to 3.7.5/3.9.0.

Downgrade does not help either.

 

(CID:143759224)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:16 PM . Last Modified: ‎2024-04-03 02:42 AM

In response to DCIM_Support
0 Likes
0
2501
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:16 PM . Last Modified: ‎2024-04-03 02:42 AM

Hi Serg,

Thank you for your reply.

You might want to doublecheck the A-link connections between the sensor pods (I am guessing that you are referring to sensor pods, when you say extension modules).

 

An A-link terminator should be in place in both ends of the cascaded sensor pods and a missing A-link terminator may cause connection problems.

 

If you are already checked the physical connections and you are % sure that there are no recent changes made physically to your existing Netbotz setup, it could be a hardware problem on the Netbotz 200 or on the sensor pod(s).

I apologize if you feel that my initial reply did not seem to help. You might want to provide the APC/SE partnumbers next time you raise a question so we can check and review the case properly.

 

I hope this helps.

(CID:143759266)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:16 PM . Last Modified: ‎2024-04-03 02:42 AM

In response to DCIM_Support
0 Likes
0
2501
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:16 PM . Last Modified: ‎2024-04-03 02:42 AM

For now I trying to revive Netbotz main module without any sensor pods.

(CID:143759276)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:16 PM . Last Modified: ‎2024-04-03 02:42 AM

In response to DCIM_Support
0 Likes
0
2501
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:16 PM . Last Modified: ‎2024-04-03 02:42 AM

If reflashing, (reapplying the firmware) does not help. It could be a hardware problem.

(CID:143759305)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:16 PM . Last Modified: ‎2023-10-22 03:15 AM

0 Likes
0
2501
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:16 PM . Last Modified: ‎2023-10-22 03:15 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore